Baxi system boiler and Opentherm
View the thread, titled "Baxi system boiler and Opentherm" which is posted in Boiler Advice Forum on UK Plumbers Forums.
Hello
Does anyone know if its possible to connect an Opentherm thermostat such as a Nest to a Baxi 800 System boiler.
I know its possible with a Baxi 800 Combi but I cannot find any information on achieving this with a system boiler.
I wondered if its possible to control the radiator flow temperature with say a Nest connected to the opentherm inputs.
(also controlling S plan CH & HW zone valves with its 240V outputs.)
Then for higher flow temperatures needed to heat the HW cylinder reliably to 60C, I would like to slightly modify the standard S plan to hot water priority with one relay (disabling CH zone valve when HW zone valve open) and add the Relay PCB kit from an Baxi IFOS System kit (without the weather comp sensor).
Its my understanding that 240V on the Relay PCB kit when installed temporarily overrides any current boiler flow temperature to 80C
Thus when the HW cylinder made a call for heat, the Zone valve to the HW cylinder would open and using a simple extra relay the central heating zone valve would close. (if it was open - the modified S plan). At the same time the HW cylinder call for heat would also cause the IFOS Relay PCB to boost boiler flow temperature to 80C.
Then when the HW call for heat ceased flow temperatures would be controlled by Openthem control and CH flow would be resumed.
Does anyone know if this would work
Many thanks
Ian
Probably not but check with Baxi technical.
There's a heating engineer on YouTube called Andrew Millward (Watford) who's adept at these sort of custom fixes, he has a very helpful FaceBook group that you can join.
Thanks for the responses,
I had hoped that the Relay PCB (from the IFOS kit) would be a way to stimulate a full heat demand for HW, regardless of whether you were using IFOS or Opentherm sensors.
Looking at the PCB layouts the Relay Pcb seems to short out the terminals on the System main boiler PCB that in the Combi are connected to the DHW NTC sensor. I am guessing the boiler figures out its in IFOS mode by geting weather sensor input then the IFOS control software looks on the DHW NTC sensor terminals for open or short ie a call for max temp flow.
In opentherm mode maybe the software does not look for/react to this input, as it does not expect it ?
However one final confusing piece of information from the Installation guide for an IFOS Kit suitable for Baxi System boilers. (page3)
"OpenTherm Controls: If an OpenTherm control is also to be connected to the boiler this must be taken into consideration as some devices affect the operation of the boiler control knobs or buttons. Depending on the device used it is possible that the OpenTherm control will assume the role of “master”, rendering the boiler controls inoperative or altering their function.
It is recommended that the IFOS is fitted and set prior to connecting any OpenTherm device. Consult the instructions supplied with such devices before setting the curve.
The Baxi uSense device is recommended for this type of control application."
So this would make for an interesting experiment ??
IFOS and Open Therm dual input was considered possible by BAXI, why would you ever have load compensation and weather compensation at the same time !!!
Any thoughts ?
The boiler knows it’s in hw mode via a cable / 240v from the hot water call to the boiler terminal block
“A 230V switched live from the DHW cylinder thermostat (demand signal) must be connected to the spare position on terminal block M1”
And then a normally open relay connected to the same hw call breaking the brown 2 port for heating
That sorts the hw side out eg high fire and hw priority
As for the nest it’s worth a try in open but you might have to switch it to just 240v switching depending on findings in theory it might work but sometimes it doesn’t play ball etc baxi and opentherm
Shaun thanks for your help,
I think I have missed something, I did not realise you could mix Opentherm and the normal switched live input.
Just to confirm are you saying that if I have an opentherm controller wired on low voltage M2 pins 1&2 this should "in theory" control CH flow temperatures. (assuming no switched live inputs on M1 pin1 )
If I then apply a HW demand as a switched 230V live to the normal switched live input on M1 pin1 the boiler will ignor any opentherm commands and fire. Do you know if this is definitely at max flow temperature or will the boiler fire at the set temperature on the CH dial - as though it was in normal switched live mode ?
Thanks again
You can’t to my knowledge but the switch live eg hw demand to the ifos box must isolate it just to that
In theory if everything is wired correctly yes
Like I said above worst case use the nest in 240v switching and plug in the wc sensor and set the curve and it will do the same as open therm but better
Thats great to hear, would you care to share more details of a typical installation.
In particular how exactly did you get the boiler to fire at higher temps to heat hot water while connected to Opentherm ?
Did you set up the system as hot water priority ?
I have also read that Baxi are not fully Opentherm compatible, did you have to setup anything special on the Evohome ?
Thanks for any information you can give, there is very little on the internet about Opentherm and Baxi 600/800 System boilers at present.
Evohome controls the flow temp, so for HW it goes in Max (80oc flow). Then back down for CH.
Got HW Priority with a NO motorised valve for CH however there’s radiator controllers on all the rads.
When Opentherm is used the controls on the front of the boiler are redundant. You can’t set a max flow temp, it’s done by the controller which will be the boilers max 80oc.
Thanks for the info, I was hoping for a simpler solution that could somehow use an Nest opentherm controller and a 230V method to call for max temperature when required. Not convinced this is possible.
Its my understanding that a Nest only has room temperature as an input, therefore it does not know if there is a cylinder HW demand unlike an Evohome that has a cylinder stat sensor for input.
As far as I can see implimenting HW priority with system boilers and a Nest (in opentherm config), requires that the Nest measures the room temperature and adjusts flow temp with opentherm. Then HW priority is externally demanded by a simple cylinder mounted stat providing a 230V switched live that can be used to switch zone valves as appropriate and if supported by the boiler - request full temperature flow. (overriding any opentherm inputs).
So far I have found no documented way for a 230V live to request a Baxi 600/800 to go max flow temp when under opentherm control.
Some Ideal boilers manage it via a S2 switched live input, I was hoping to find a Baxi work arround no luck yet.
I am surprised that Baxi make it so difficult to impliment HW priority with Opentherm CH control on their system boilers.
Haven't tried it, but perhaps the normal Live overrides the Opentherm. I think I had to remove the 230v link for the Opentherm to work, however I can't remember.
Baxi have their own controls that use the Opentherm protocol.
HW priority is easy to set up with just relays.
On the whole I think theres numerous issues with Nest and Opentherm with a number of boilers.
I have spoken to Baxi technical support and they have confirmed that you cannot use the standard switched live input and Opentherm together on a Baxi 600/800 System boiler. You have to use either Opentherm OR Switched live.
Using both will confuse the boiler.
So as far as I can see, if I want Opentherm controlling CH flow temperatures the only solution would be a suitably configured Evohome with Opentherm controlling CH&HW flow temperatures and the zone valves.
Unfortunately this works out considerably more expensive and complicated than I had hoped. I suspect I will just go the switched live route with a smart thermostat and possibly consider adding the IFOS system kit.
I have been doing some further investigation of Opentherm controls for system boilers focused on controlling both Heating and the temperature of a hot water cylinder.
I have been looking for a cheaper solution to the excellent Evo Home and think I might have found it by using a couple of products from EPH that allow you to combine the Opentherm signals from a Room thermostat and a HW cylinder thermostat.
The two devices are a:
CP4i Opentherm Smart Thermostat (with an RF1A-OT control receiver)
CP4-HW-OT Opentherm programmable cylinder thermostat (with an RF1A-OT control receiver)
The two thermostats each come with a RF control boxs that can control a zone valve and be easily wired together to give hot water priority.
The RF control boxes can also be linked by RF so that one of the control boxes can be defined as the Opentherm Hub. The Hub will then send Opentherm commands from both thermostats to a System boiler over just two wires. (further room thermostats can also be added if more heating zones are required - sending its opentherm commands to the defined Hub)
As a bonus a Wifi gateway (GW03) is available that allows all devices to be controlled over the internet if required using the Ember app.
This solution seems to tick all my requirements to fully control a system boiler by Opentherm for:
central heating, cylinder hot water, relays for zone valve control, priority HW and internet access at a very reasonable price.
I am about to give it a go but am interested if anyone else has used these EPH thermostats in a combined Opentherm configuration giving priority hotwater with a a Baxi 600/800 system boiler.
I’ve used eph controls and there great might want to email tech just to check product numbers etc
I thought I would give an update in case anyone else wants to implement full Opentherm control of a Baxi 600/800 System boiler using a simple low-cost approach.
I have been using the EPH controls mentioned in my previous post for a while now controlling a Baxi 818 system boiler that is plumbed hot water priority using a 4043B (normally open) valve for heating and a 4043H (Normally closed) valve for hot water.
It’s all working perfectly, HW always uses the max set flow temperature which I have set to 70C and CH in my case typically ranges between 65 and 47C depending on room demand (it gets to 55C or below quite quickly). A range of Opentherm parameters such as max, min flow temps are user definable and you can monitor flow/return and boiler modulation via any connected thermostat.
(My Opentherm user set flow temps are Max 70C min 45C)
I chose the normally open valve on the central heating as it ensures there is always a “bypass” route for the boiler through the central heating circuit when the boiler goes into pump over run at the end of any heating cycle (HW or CH - rather than being restricted to the boilers limited internal bypass)
Should you wish, you can modify the wiring slightly and use two normally closed valves to easily use the above setup with a standard S plan arrangement. (This is detailed on the EPH website under hot water priority).
With the additional Wifi gateway I can control heating and hot water over the internet from the Ember app - which also works very well. A point to note is that for safety HW storage temperature can only be manually set at the EPH tank thermostat.
I have been very impressed how well this all works, it’s been completely reliable and controls the boiler very efficiently with the boiler on very low for long periods. It keeps the return flow temperatures well below 54c during room heating cycles and heats my current hot water cylinder using 70C in approx 30 mins.
(I should add in my case when heating the HW tank using 70C flow, the return temps are over 54C but thats probably due to my current tank and is only for 30 minutes)
All at a very reasonable price of around £200.
Hi Ian, sorry to restart an old thread, I wondered if your system is still working fine.
from what I have read Baxi are not members of opentherm association and their boilers aren’t fully compatible with open therm products as the opentherm signal from the controller has to have an ID for Baxi to recognise it.
It does sound like the set up you have from EPH works properly with the Baxi boiler though - could you confirm if you’ve found that to be the case?
TIA
TIA
Hi sorry to be so slow in responding.
The setup I described in my previous post has been totally reliable, I have not had a single problem with it since I installed the EPH controls back September 2022. I have been very impressed with the EPH setup for HW priority control of a Baxi system boiler.
Let me know if you want any more info
Rgds
Ian
Thanks to @Ian777 - I've just ordered EPH Combipack 4, a separate cp4i for a 2nd heating valve and the cp4-hw-ot for cylinder stat based on your post for my new Baxi 830 system 2 which is now officiallyopentherm certified. I've looked into all the other controllers on the market that support opentherm but only the EPH controls support opentherm plus 2 heating zones and a hw cylinder on a system boiler
Reply to the thread, titled "Baxi system boiler and Opentherm" which is posted in Boiler Advice Forum on Plumbers Forums.
Ian777,
Harp62,