Hi,

A customer wants cast iron style rads throughout, 9 or 10 in total but currently has 10mm pipe .

Is there any problems installing this type of rad on mircobore? I'm worried about the water content being much higher and it not circulating?

Anyone else installed these on mircobore?

Cheers
 
Typically are they not a high water content beast? If so, I don't know how you'd get sufficient flow...
 
Surely the water flow required is related to OUTPUT, not water content? Agree that a CI rad will contain a lot of water and take a long time to heat up, but a 2kW rad requires a set amount of water, regardless of the water content, otherwise the system won't be balanced properly. So I'd argue that the fact that the radiator is cast iron is largely irrelevant.
 
Surely the water flow required is related to OUTPUT, not water content? Agree that a CI rad will contain a lot of water and take a long time to heat up, but a 2kW rad requires a set amount of water, regardless of the water content, otherwise the system won't be balanced properly. So I'd argue that the fact that the radiator is cast iron is largely irrelevant.

Just come to this thread and above ^ was also my first thoughts.
I think a cast iron rad fed by 10mm will take a very long time to reach full heat because it has large water volume, but will maintain output once reached and then rad will hold heat longer once off.
Personally I would go with steel cast iron lookalike rads.
 
Hmm. Output can only be maintained if more energy is input than can be output. The larger the mass of water, the more sensible energy it contains. If the rad dissipates more energy than the volume of water can supply then it simply cannot do its job and complaints ensue - even tho you've told them.

You would normally slow down flow to improve heat transfer but doing that means you may not move enough mass through in a 10mm system bearing in mind 10mm is the external dia not internal. Other factors mean its usable bore is probably more like 7mm max. This means warm one side cooler the other.

I'm with Harvest on this one. 12mm copper borderline, 15mm copper to make certain. 😱
 
  • Like
Reactions: Harvest Fields
I don't know, all I know is I see loads of microbore and unless it full of magnatight it works, I don't like it but it works.

And my view on flow is to restrict down as much as possible on the lock shield, so the hot water in rad has time to give off it's heat.

Not really my area tho.

Nb . Bungalow, 22mm circuit in the loft with microbore tee offs, not on a manifold.
 
I don't know, all I know is I see loads of microbore and unless it full of magnatight it works, I don't like it but it works.

And my view on flow is to restrict down as much as possible on the lock shield, so the hot water in rad has time to give off it's heat.

Not really my area tho.

Nb . Bungalow, 22mm circuit in the loft with microbore tee offs, not on a manifold.
Change the dogs legs to 15mm in the loft and run them in the corner of the room in trunking under the floor and up into the rad.
 
Cast iron, or that style, will look stupid with 10mm pipes anyhow. I wouldn't do it unless with a total repipe.
People want luxury look with poor pipework supply.
Bit like putting a Ferrari body on a Sinclair C5.


I know, but it's all dropping down from the loft, might be happy to pay for chiselling in, I've not asked, and I've no idea how long that would take???
 
I know, but it's all dropping down from the loft, might be happy to pay for chiselling in, I've not asked, and I've no idea how long that would take???

Take ages even using a wall chaser. I have done that when piping to ordinary rads, but the lack of movement in the pipes to the rad valves is then a problem.
 
  • Agree
Reactions: 1 person
Take ages even using a wall chaser. I have done that when piping to ordinary rads, but the lack of movement in the pipes to the rad valves is then a problem.

How long per rad to chisel out and put copper in???, bungalow and I'll have ex BG installer with me, (I'm a service and repair guy, so slow on pipework, Just slow all round really)
 
That's what the customer mentioned, it's probably the best compromise, but pipes coming out of the skirting still looks a bit **** I think.

Ffs, installing is hard!!!
I wouldn’t do it. But it’s an option. I would chase the wall or floor. Wall is the easiest option.
 
It depends on the size/surface area of the radiator and the delta T.

They will govern the required water flow rate/speed/volume required.

That will determine the size/bore of pipe required.

There are other things to consider when designing a system such as frictional resistances through pipe work, pump sizes, water noise etc but I am presuming that all that is correct and you are just changing the radiators.

I agree with other comments about the aesthetics.

Those type of rads were not really seen (in real life), with 10 mm pipes sticking out of walls.

Customers!!
Fashion!!
 
It depends on the size/surface area of the radiator and the delta T.

They will govern the required water flow rate/speed/volume required.

That will determine the size/bore of pipe required.

There are other things to consider when designing a system such as frictional resistances through pipe work, pump sizes, water noise etc but I am presuming that all that is correct and you are just changing the radiators.

I agree with other comments about the aesthetics.

Those type of rads were not really seen (in real life), with 10 mm pipes sticking out of walls.

Customers!!
Fashion!!


Ffs, customer just rang after I put in my ball park quote, rads to expensive going with white panel ones.
 
I think I hired a chaser for £40. But I had my own vacuum.
Agree 2kW is probably too much on 10mm - in any case, 2 kW was a figure plucked out of the air, not an actual figure relating to the OP's question.
 
  • Agree
Reactions: 1 person
The only thing 10mm should be used for is oil line every time I come across it I remove it
 
The only thing 10mm should be used for is oil line every time I come across it I remove it
Then you are in disagreement with the Copper Development Association which states:

Where
the chosen diameter is too large, so
that the velocity is less then 0.5 m/s,
then sludge can settle in the piping.

and in some cases would therefore prefer to see 10mm used to get sufficient velocity.

Of course, you are allowed to be in disagreement, though.
 
  • Agree
Reactions: Last Plumber
Then you are in disagreement with the Copper Development Association which states:

Where
the chosen diameter is too large, so
that the velocity is less then 0.5 m/s,
then sludge can settle in the piping.

and in some cases would therefore prefer to see 10mm used to get sufficient velocity.

Of course, you are allowed to be in disagreement, though.

I agree.
There is no need to over size pipework and no excuse for under sizing it.
 
. . . and every single one of them is right?
No.
They are not all right.
Pipe size can and should be calculated out.
There are 'rules of thumb' of course and we all use them but they come from experience normally. Experience of everyday /common work.
 
  • Agree
Reactions: Dkdc71
Our house was done with 8mm years ago. I was skeptical and promised myself I would redo in 15 but actually works OK even on large k2. Yes takes a while to heat up but maintains fine, just depends on lifestyle. So never got around to changing. If they just want fast short bursts of 2 hours morning and a few in evening then might struggle.
 
I'll ring the manufacturers tomorrow , try and get something in writing .😉😉😉
Here's a link to a manufacturer who feels microbore's OK FAQ's Questions Cast Iron Radiators | Ribble Radiators
The 10mm can be disguised or concealed if the aesthetics are a big issue. I had an 1800 x 600 double convector running satisfactorily on 8mm microbore for 34 years at our house, installed from new in 1977 by the developers (until the in screed F&R pipes succumbed to corrosion...) Instinctively, it feels wrong, but it worked.
 
I do note the very careful phrasing used. 'can' be used. That is a world away from operate at full effeciency, or perform just as well kind of thing. Id wager 10 hard earned pence they would only say "at a push"...
 
I do note the very careful phrasing used. 'can' be used. That is a world away from operate at full effeciency, or perform just as well kind of thing. Id wager 10 hard earned pence they would only say "at a push".
I know what you mean, I only provided the link so that the original poster could, were he to so choose, investigate further. (and I might benefit when he posts the results)
 
  • Like
Reactions: Welder
In fairness, years before I was qualified, I used a mixture of 22 Cu, 15 Cu and 10mm Hep to make a manifold heating system where I was living. The 15 was for a DPDC rad that needed more than 10. The 10mm Hep was for everything else. The 22 was to the manifold (which was, itself, made from 22), and the cylinder.

According the the pipe sizing method of the Copper Developmnent Association or whatever it's called (as previous post) that I used (a slightly simplified version to the City and Guilds Level 3 textbook method IIRC), 10mm was excessive for some of the rads, but I wasn't going to buy yet another roll of pipe for the smallest rads.

It actually worked very well indeed. Since there was minimal water content in the pipework, the rads warmed up quickly. Since the system was to some extent balanced by the resistances in the flow and return runs being roughly equal prior to any fine tuning using the lockshields, the system balanced quite easily and, since none of the lockshields needed cranking down massively, the system ran quietly. The pump was an old UPS 15-50 on the lowest speed to allow a 10°C drop. This was in a three-bedroom, 8 radiator house.

If I'm working on an existing system, using 15mm gives me a margin of safety that allows me to know my pipework is not restrictive. This is useful if a larger or additional radiator is later substituted, or where I do not know how the runs are made, how much available head there is, etc. But, if I were starting from scratch, I have no problems with microbore - I have seen it work very well. The only problems IMO is that the system needs to be kept clean, that microbore is more vulnerable to damage than half-hard 15mm, and that, visibly connected to a fat old iron radiator, it might look a bit strange.

I maintain that flow rates should not be a problem if the pipework is sized as it should be.

Take Classic 3 Column Cast Iron Radiators 500mmRRP 17 and use a 500 high by 630 wide radiator (10 section) as an example. Output is 1800btu, which is about 0.5kW. Conveniently (saving me looking it up properly), this link (http://copperalliance.org.uk/docs/l...eating-systems-pdf.pdf?Status=Master&sfvrsn=0) suggests 5kW at an 11°C drop needs 109ml/s which is 6.6l/m. So a 0.5 kW radiator needs only 0.66l/m: a mouse's fart. On 10mm, the loss of head for a 0.5kW radiator running at an 11°C drop, is a mere 0.006 metres per metre run of copper pipe. In fairness, we tend to use a 20°C temperature drop these days, and there are other factors involved, so this is only an approximation, but you see my point. By all means shove more water through the radiator than its output requires to allow a fast warm-up, but be aware that the condensing boiler will not then run in condensing mode, and the pump will be using more electricity than it needs to.

You'll then use the lockshield valve on the radiator to reduce the flow to the 11ml/second that the 0.5kW radiator actually needs... and the radiator will take LONGER to warm up because of the slightly increased water content of the system.

As others have said, the point is to size the pipework properly. Too fat a pipe will be less of a problem than too thin a pipe, but the ideal is a properly sized pipe.
 
  • Agree
Reactions: doitmyself
Only time we would come across 10mm on a heating system was when it was an old system with blockages and not working properly haven't seen it been used on a new system in 25 Years half inch is the standard for rads here
 
That's what I mean last time I know of a house piped in it was also built in the 80,s mother in-laws house had it end up repiping the heating every time I would visit she would say one or two rads not working got a pain in the arse listening about it redone it and never a problem since, we were told in college back in the 80,s there was a shortage of copper pipe at the late 70,s the price was too high for lengths so that's why it was used we were told I came out of my apprenticeship in 88 and never once piped a house with it only came across it over the years
 
No, I meant houses built SINCE 1980. Including noughties houses ( the plumbing in these has generally been awful, but no flow issues in the ones I have worked in, even though they were in 10mm).
 
  • Like
Reactions: Dkdc71
Over here 1/2 inch would be the standard practice for the rads as I said when came across it we would remove generally blocked ,do you remember the same end twin feed rad valves .absolute Rubbish last job we came across it was in very expensive houses in Dublin city a builder came in and removed a rad to put patio doors in and just turned the valves off and buried them in concrete no rads would work it was effectively a one pipe system and with the rad removed it wouldn't work Rubbish job for a 1,000,000 pound house plumbing just as bad a lot of cowboys around then and not enough sherrifs
 