If the stat is not shutting off a combi boiler (analogue stat Honeywell) even though the stat is clicking when turned up above the room temperature. What are the likely causes. Unless it's never been wired right from the start up. Thanks.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Just going to download the instructions. But to test would I be looking to see if I get 240v between live and switch live?As Shaun and I say get your multimeter out , simple enough mate.
No mate, testing that you’ll probably get 120vac.Just going to download the instructions. But to test would I be looking to see if I get 240v between live and switch live?
Yes correct, but doesn’t prove it works properly, hence the additional testing and don’t forget the link.Thanks so testing neutral to live in. With a reading of 240vac between the ports. Shows I am getting 240vac to the stat.
YesDoes testing neutral to switch live on demand with a reading of 240ac show that switch live is sending power to the boiler. Making a circuit when there is a call for heat?
Thanks yes I will make sure it's wired in to the boiler.Yes correct, but doesn’t prove it works properly, hence the additional testing and don’t forget the link.