Correct size of radiator for BTU calculations
View the thread, titled "Correct size of radiator for BTU calculations" which is posted in DIY Plumbing Advice on UK Plumbers Forums.
Hi I’ve done a BTU room calculator, going by the calculations I need a radiator 6407 BTU, and 1877 watts. I’ve found a radiator just over these calculations at 6581 but in the description delta T65 is 6581. Delta T50 is 4695. Delta T30 is 2433. I have a recently fitted combi boiler. Would this radiator be fine for my room? Or do I need the T50 readings to be the same as my room calculation? Thanks for any help 👍🏻
Needs to be dt34 or dt29
So dt50 size would be 10.5k btu
So would the one above not be sufficient for my room?
If I calculate my room at 6407, what reading of radiator should I be looking to buy?
I’m pretty confused as tried a few different calculators and they’ve all gave me totally different readings ranging from 3000 to 6000. Thanks
Should I be looking for a rad with (delta t50 10.5btu readings) even though the calculator says I need 6407btu? Cheers
Yes output at dt50 of 10500btu / 3kw
Problem is that doesn’t take in your flow and return temperatures that’s just your heat loss
Dt50 is for an old school boiler high temperature eg 75-80c
As you have a condensing boiler your temperature will be 60-65c
If the calculator says I need 6407, why would I choose one higher than that?
Because your emitter size is different to your Heatloss
As you know the heat output varies with different mwt/at-dt
Condensing boilers need a dt 34 max else you won’t have any efficiency/ energy savings and will decrease the boiler life
If you want a good read have a look at part L
Would you have a link for a vertical radiator that’s 10,500 btu, I can’t seem to find any that’s at 10.5 btu at dt50. Thanks for the quick reply’s 👍🏻
Reply to the thread, titled "Correct size of radiator for BTU calculations" which is posted in DIY Plumbing Advice on Plumbers Forums.
Glasgowman,
Glasgowman,