My experience with Opentherm with Vokera is not very positive. I have tried on three separate systems to integrate the former Honeywell Evohome system with Vokera products. The results have been unpredictable and in one system led to lockouts on overheat.

I am sure that these issues are resolvable - but it is not plug and play - which is what I need to sell systems that are seamless in their compatibility.

Others probably have had better experiences

Thank you for this info. I think I will just leave it un-connected. With the modulation and other control aspects of the boiler, together with the Wiser system, I think I will be 95% of the way there.
 
eg: You come back from holiday in mid-Jan, and it's minus 5C outside. The heating has been off for 3 weeks, and everything is stone cold. So you want to heat the CH water as quickly as possible, and the radiators are shedding large amounts of heat, as the rooms are so cold.
You are forgetting that a heating system is sized for exactly those conditions (though usually -3C outside). It doesn't assume that the internal temperature has only dropped (e.g) five degrees. If the heat loss calculation says you need a 15kW boiler, you need a 15kW boiler;.fitting a 30kW will not achieve anything. But if you have a combi which produces 30kW for heating, then range rating down to near 15kW would be a sensible thing to do.
 
We shouldn't forget that if the system is down overnight then the boiler must reheat say 75/100 litres of water from say 20C to say 70C which requires ~ 4.4 kwh minimum, as this is being heated up, the rads will start emitting heat as well but it does take extra time to achieve full operating temperature, my ~ 15 kw heating load with 85 litre of water heated by a 20kw oil fired boiler takes 25 to 35 minutes in the morning before reaching 70C and cut out.
 
You are forgetting that a heating system is sized for exactly those conditions (though usually -3C outside). It doesn't assume that the internal temperature has only dropped (e.g) five degrees. If the heat loss calculation says you need a 15kW boiler, you need a 15kW boiler;.fitting a 30kW will not achieve anything. But if you have a combi which produces 30kW for heating, then range rating down to near 15kW would be a sensible thing to do.

This is such an interesting conversation, and much appreciated.

From my (limited) understanding, my property's heat loss, is calculated at an external temp of -3C and in internal temp of 20C. Let's say for example the total is 13kW. My boiler will need to run, on average, at 13kW to maintain this constant internal temp of 20C, assuming all other factors, including the external temp of -3C remain constant.

But if we now consider the conditions I outlined above namely: -5C outside and -5 inside — due to leaving the house empty and unheated during a 2 week cold-spell. With this scenario, when I return from holiday, I now wish to heat the house as quickly as possible to reach 20C, and so the boiler can ramp-up to 30kW, and then modulate down to 13kW when 20C is reached?

In practice, the boiler would only increase its output so the flow temp maxes to say 80C; and the radiators would be able to shed far more heat, as the delta is now D78 and not D50 (or even lower). (Av rad temp of say 75C, and an internal temp of say -3, gives a delta of D78).

Any thoughts? Is this a correct analysis?

Hence why, it seems, that when you have a modulating boiler, you don't need to range-rate it, and indeed if you did so, it would not make the boiler as useful and as quick to rapidly heat the house when you needed to.

Of course, I understand that in practice, you would be better to perhaps leave the heating on at a low-level whilst you are away for a number of reasons.

Thanks!
 
Last edited by a moderator:
If you de rate the boiler to match the heating load, say 13kw above and you come home to a freezing house, and because you want a reasonable quick heat up in some rooms initially, then simply just heat the ground floor for a hour or two, you will then get a very rapid heat up to operating temperature and then the boiler will modulate to maintain this heat load of ~ 50%, then switch in your second zone and this will heat up, at a slower rate admittedly but you won't suffer any great discomfort IMO. In practice, I don't think anyone really sets the boiler output to exactly match the heating load. If it was my house and I had a 30kw boiler with a 13kw heating load I would de rate to maybe 18 to 20kw.
Also the de aerating isn't written in stone and is settable and I think in some cases the user can select his heating output from a menu?.
 
But if we now consider the conditions I outlined above namely: -5C outside and -5 inside — due to leaving the house empty and unheated during a 2 week cold-spell. With this scenario, when I return from holiday, I now wish to heat the house as quickly as possible to reach 20C, and so the boiler can ramp-up to 30kW, and then modulate down to 13kW when 20C is reached?
Assuming the system stills works at all and hasn't been destroyed by freezing, it would depend on the design of the radiator system, i.e. size of radiators and how they are piped. A system designed to emit 15kW max (at say 60°C flow) is going to struggle to emit more than about 23kW max (at say 80°C flow)

The 'perceived temperature' of a house depends roughly 50:50 on the air temperature and the temperature of the surfaces. You can get the air temperature up fairly quickly (hours) but warming the fabric of the building can take several days.

I'd recommend that you leave the house with the heating set at 10°C and the stopcocks off.
 
  • Like
Reactions: david007
From my (limited) understanding, my property's heat loss, is calculated at an external temp of -3C and in internal temp of 20C. Let's say for example the total is 13kW. My boiler will need to run, on average, at 13kW to maintain this constant internal temp of 20C, assuming all other factors, including the external temp of -3C remain constant.
The boiler will not need to run at 13kW once the house is up to temperature.

Let's say the house has got up to temperature so the room stat has turned the boiler off. The room temperature starts dropping and when the temperature has dropped, say 2C, the room stat turns the boiler on. The boiler now needs to raise the temperature by 2C, not by 23C (from -3 to 20), so only 1.13kW is required (2/23 x 13). Unfortunately most boilers only modulate down to about 5KW.
 
The boiler will not need to run at 13kW once the house is up to temperature.

Let's say the house has got up to temperature so the room stat has turned the boiler off. The room temperature starts dropping and when the temperature has dropped, say 2C, the room stat turns the boiler on. The boiler now needs to raise the temperature by 2C, not by 23C (from -3 to 20), so only 1.13kW is required (2/23 x 13). Unfortunately most boilers only modulate down to about 5KW.

But 13 kw is still required to maintain the house at 20C (from -3)? , last night (ambient -1C) with downstairs zone only on and with roomstat set to 22C, my 20kw boiler (oil) was cycling and burner firing for 35% of total cycle time which means my heating demand was 7 kw, this was with the roomstat switching between 22C/19C, if I had had a modulating gas boiler then I would expect it to operate continuously at 7 kw output with a boiler temperature (my SP) of 70C and would obviously stop firing with roomstat switch off, then resume firing when roomstat again calls for heat and would fire at 100% output until boiler SP again reaches reaches 70C so IMO yes it will only take a few extra kw(H) to restore the balance but at no time will its demand fall below 7kw? as long as the ambient conditions don't change, the same should apply to any heating demand.
 
Last edited:
why not just switch to a Japanese combi and be done with any guessing. Everything is included in the price and so much more. Prices are around £1000 inc VAT and delivery (and flue and fitting kit and IoT controller (that even talks to you lol)
 
But 13 kw is still required to maintain the house at 20C (from -3)?
No. All that is required is sufficient heat to make up for the drop in temperature due to the hysteresis of the room stat.

If you need 13kw to raise the temperature 23K (-3C to 20C) that is 13/23 = 0.565kW/K. So for a room stat with a 3K hysteresis that means 3 x 0.565 = 1.7kW (approx). But you say you need 7kW. How did you measure the 35%?
 
Are you saying that it only takes 1.13 kw to maintain the house at a average room temperature of 19C ((20+18)/2) with a outside temp of -3C, once its up to temperature.

I'm afraid I don't get that, think of it another way, we are told that a house needs 13kw to maintain the house at 20C., IMO if you rise the roomstat slightly above 20C then the boiler still requires to run at a constant 13kw to maintain 20C, if you reduce the roomstat to 20c then the boiler and circ pump will cut out but the rads are still emitting a lot of heat, 13 kw at the time of cut out but the emittance will then fall with reducing rad temperature leading to reduced room temp and the boiler will cut in again at 18C and will again eventually get the room temp up to 20C and so on but the average energy required is still 15kwh or slightly less or the required power/hour is 15kw and not 1.13kw.

Re my measurements, if the roomstat isnt satisfied I just measure the burner run time (its quite noisy) and the off time, I do this for just a few cycles and divide the total run time by the total cycle times and that gives me a % which I X by the boiler output of 20kw. If I want to measure the average demand with the roomstat cutting in/out, I do it over a extended period of say 1 hour with a plug in energy monitor which measures the fan/burner power for that 1 hour run period and from that I can calculate the kw(h) required which is a bit less but only a 1 or 2 kw(h) or so over that period.
 
we are told that a house needs 13kw to maintain the house at 20C.
That's not how I understand it. 13kW is the boiler output required to raise the temperature from, say -3C to 20C. It's the temperature difference which is important, not the target. So if the outside drops below -3C, say to -6C, the room will only get up to 17C, not 20C.

IMO if you rise the roomstat slightly above 20C then the boiler still requires to run at a constant 13kw to maintain 20C, if you reduce the roomstat to 20c then the boiler and circ pump will cut out but the rads are still emitting a lot of heat, 13 kw at the time of cut out but the emittance will then fall with reducing rad temperature leading to reduced room temp and the boiler will cut in again at 18C and will again eventually get the room temp up to 20C and so on but the average energy required is still 15kwh or slightly less or the required power/hour is 15kw and not 1.13kw.
Sorry, but I just don't follow your logic.
 
That's correct, as the boiler output was based on the heat loss based from -3C to 20C, if you think the temp might drop to -6C you size accordingly plus as I suggested a margin of ~ 5 kw or so as you must heat up the system contents as well each time from cold and also it must be borne in mind that after the rads are up to full temperature the house temperature is not so the rads will emit even more, hence the need for that margin. IMO.
So again, based on the specified 13 kw requirement from -3C to 20C, do you still reckon that it only takes a little > 1 kw to maintain this house temp, I wish I had a house like that.

My logic tells me that once my house, once the system contents are up to temperature, that it will require 13kw to maintain it as it is loosing 13kw to the outside.

[automerge]1607110765[/automerge]
You are forgetting that a heating system is sized for exactly those conditions (though usually -3C outside). It doesn't assume that the internal temperature has only dropped (e.g) five degrees. If the heat loss calculation says you need a 15kW boiler, you need a 15kW boiler;.fitting a 30kW will not achieve anything. But if you have a combi which produces 30kW for heating, then range rating down to near 15kW would be a sensible thing to do.

Here is the specification based on the heat loss..
 
Last edited:
Some fundamental misunderstanding here. 13kw is the amount of energy required to maintain the internal temperature at 20 when the outside temperature is -3.
It is the heat loss of the building.
I’m afraid your “only needs 1.13kW “ is incorrect - assuming your numbers were right it would be 1.13 + 13 approx; not just the 1.13
Have another think...
 
  • Like
Reactions: John.g
Some fundamental misunderstanding here. 13kw is the amount of energy required to maintain the internal temperature at 20 when the outside temperature is -3.
It is the heat loss of the building.
I’m afraid your “only needs 1.13kW “ is incorrect - assuming your numbers were right it would be 1.13 + 13 approx; not just the 1.13
Have another think...

Many thanks for that, and even I, a humble member of the public agree.

And surely it must also be correct, that if this delta 50 heat loss of the building is 13kW (-3 temp outside, 20 inside), then if you need to heat the whole house from -3 to 20, then have a boiler that can run at 30kW is going to help. And it is going to be able to run at much more than 13kW, because the delta of the rads is now 73, and even 83 if you up the flow temp to the max of say 80C. ie: the rads are going to be able to shed far more than 13kW of energy, until the inside temp reached 20C.

Hence, if you have a self-modulating boiler, then you not only don't want to range-rate it; but doing so will actually slow down the speed at which you can heat-up a really cold house.
 
Some fundamental misunderstanding here. 13kw is the amount of energy required to maintain the internal temperature at 20 when the outside temperature is -3.
It is the heat loss of the building.
I’m afraid your “only needs 1.13kW “ is incorrect - assuming your numbers were right it would be 1.13 + 13 approx; not just the 1.13
Have another think...

Or maybe, at 18C the heat loss is "only" 11.87kw and 13 kw will restore the balance again at 20C.
 
Some fundamental misunderstanding here. 13kw is the amount of energy required to maintain the internal temperature at 20 when the outside temperature is -3.
It is the heat loss of the building.
I’m afraid your “only needs 1.13kW “ is incorrect - assuming your numbers were right it would be 1.13 + 13 approx; not just the 1.13
Have another think...
If 13kW was requred to maintain 20C continuously inside, the boiler would have to run continuously. But it doesn't. The boiler is turned off when 20C is reached, and turned back on when the temperature has dropped, say 2C. All that is now needed is sufficient heat to raise the temperature by 2C; which isn't 13 kW.

If you wanted to heat the house to 18C, instead of 20C, (raising by 21K instead of 23K) you would only need 13 x (21/23) kW = 11.87 kW. If you now wished to raise the temperature to 20C, do you have to supply another 13kW on top of the 11.87, i.e 24.87 kW?. No. you have to supply an extra 1.13 kW.

As an analogy, think of a car. To get from 0 mph up to 70 mph, in a reasonable time, requires much more energy then maintaining a constant 70 mph. And if the speed drops by 2 mph you only have to supply a little bit extra via the accelerator to get back up to speed again.
 
"If you wanted to heat the house to 18C, instead of 20C, (raising by 21K instead of 23K) you would only need 13 x (21/23) kW = 11.87 kW. If you now wished to raise the temperature to 20C, do you have to supply another 13kW on top of the 11.87, i.e 24.87 kW?. No. you have to supply an extra 1.13 kW."

Reflect on this:

You range rate your boiler to 11.87kw and wind the room stat up to 30C, what happens?, the boiler will run continuously until the house temperature reaches 18C but because the house is loosing exactly the same, then the boiler will still run continuously to maintain this 18C but the temperature cannot rise any further.
You now want a house temperature of 20C so you wind up the boiler to 13kw, what happens?, the boiler now has another 1.13 kw to get the house temp to 20C, from 18C (which requires 11.87kw continuous) it can't rise the temperature any higher after reaching 20C but will continue to run continuously at 13kw as the house is loosing exactly the same.
Having the room stat set to 20C will result in a average house temperature of 19C with a resultant average boiler demand of 12.15kw but in cycling mode.
 