if i have not got enought of my own boiler problems the guy i sometimes help out called last night - a customer of his has complained the water is not as hot as it used to be . he spoke to baxi and they advised changing plate and hw thermistor which he has done and still the same - they then said gas valve and he did - boiler still the same .he said on htg the flow pipe gets to 80 degrees but when on hw full flow the flow pipe only gets to 53 degrees (60 degrees if tap reduced to half flow ) i have never checked the flow pipe on a boiler when in hw so not sure if this is ok it could be good heat transfer to the water in plate and good circulation) i told him to test the cold water inlet temp and the hot outlet and if hes getting a 35 degree rise then the boiler is ok . also check the htg thermistor / work press / gas rate /. anyone know what temp to expect on the flow pipe in hw mode i assume it should be above 70