OFTEC figure I was given is not to allow C0 go above 90, preferred C0 figure to aim for is below 50 on condensing boilers.
 
As far as I know they are using BS 7967 I don't see the actual figure of 90 ppm in the OFTEC manual I remember from the OFTEC course.
 
Just to add something to this.
A maximum 200ppm CO is a limit BG work by.
Worcester also state this limit for their boilers.
 
Hahaha i remember something about 200ppm but cant think where from, dont beat yourself up. im on the case and i'll try to find where i read or heard it from..
 