gas rating cooker
View the thread, titled "gas rating cooker" which is posted in Gas Engineers Forum on UK Plumbers Forums.
diablo13
Hi guys, i am fairly new to the gas side of things and have a question ;i need to gas rate a cooker for commissioning and have done quite a few hobs but this is an oven/grill/4 ring appliance that gives one gas rate on the badge, do i rate each section seperately (ie grill on its own) on full aiming for the same rating on each section or all on at once or another combination.I should probably know but dont remember it coming up at college.Cheers
technically you should gas rate each thing on its own if you have the heat input of each from the MI's, (the reason behind it is one bit could be over gassed and one bit under cancelling each prob out by giving the correct answer, haha the troops who do real work will tear me apart for this one)
however the reaality is not enough people do gas rates ayway, so if you do the whole lot at the one time and get the right answer you are doing more than most, if you dont get the right total you will need to do them individually to suss out whats wrong, but again in the real world i would hope you would pick up the fault from the visual, like any other appliance it needs to be rated on max so turn up full and open the oven door to keep it lit
Because we were told in college if an appliance is over-gassed it can produce dangerous levels of CO
A cooker gas rate is not adjustable so as long as the inlet pressure is correct then the gas rate must be correct unless it has incorrect injectors fitted.
If that was the case then the flame size/picture would make further investigation obvious.
fair point , some people gas rate some dont some people just jot down whats on the data plate
I usually just fire the burners on and add the individual ratings up from MI's. Cooker/oven as long as all looks good job done.
I have came across the odd appliance that has no specific rate in MI's for oven/grill anyway.
I did a job before where a second hand cooker was being installed , I had to find a load of leaks in this big victorian house which took me 2 or 3 days , I eventually connected the cooker only for flames to come roaring out of it , The customer was screaming at this stage as her ex had given her this cooker in the first place
how do you check inlet pressure ? has cooker got test point ?
some cookers have the test point on the rig to burners and taps. My boss sometimes just usually put the manometer over the injector with 3 rings on
so when gas rating a cooke ron full, do you open the cooker door and turn on full, the grill on full and 3 hobs on all at the same time?
Theoretically yes, but it would be very unlikely that all of a cookers burners would be firing at full rate for any appreciable period, if ever.
The word applicable in the world of sparks is 'Diversity'
here's a tip for checking inlet / working pressure at cookers or hobs, keep hold of an injector from an old cooker that you have taken out, round off the hex and solder it into the brass sleeve from an old universal thermocouple. when you are checking working pressures, replace one off the injectors with this diy device. most plumbers just hold their manometer hose on the jet but this device can save gas leaking from the hose, especially when you have the other 3 burners lit at the same time.
Previous post was describing a method if determining working pressure, nothing to do with gas rate.
holding the hose on an injector, i stopped doing this when my hand almost set a light..
i look at flame picture on the hot plates and always analyze ovens.. few ovens ive checked have looked ok, but the co has been over 500ppm
cookers are the biggest killers, so i'd rather just analyze as much as i can rather than gas rate it..
if you dont put your manometer hose onto the injector, how do you know if the working pressure is correct, and what working pressure do you write down on your paperwork. the diy device i described previously ensures your hand does'nt get set alight. it's an ideal device for checking working pressure, it's not for inlet pressure or gas rating though.
Question: 1) Do you have to Co/CO2 ratio on a gas cooker? Is this a legal requirment now.
Cookers kill more people than O/F appliances? Pish!
Data badge / mi tells u output of each ring and oven. Gas rate with min 3 burners ( add up output to gas rate)
Why do you gas rate with 3 burners not max?
Using 3 burners is how you check working pressure of the meter regulator if using a cooker, any other appliance you use it on full
If u use 3 u can bp at same time as gas rate. Each burner has its own input value. U test a fire front then bbu or both at same time,?
Fair enough, if you are using 4th as well, some appliances don't have individual inputs for each ring,
On BBU, I rate boiler, then fire then both,
I fitted a Hob fired it up it looked a right treat it was bound for ukraine some how ended up here they use 16mb over there the customer service department from gorenje shouted at me and told me all gorenje hobs come with G20 UK jets . I slammed the phone down cut it off charged them and told them to contact gorenje Due to the poor cust service and a disappearing rep the hob is now a display piece Still waiting for UK Jets
Reply to the thread, titled "gas rating cooker" which is posted in Gas Engineers Forum on Plumbers Forums.
diablo13,
TFGplumbing,
