Good advice given in the posts above, however a tightness test is not mandatory when carrying out an LGSR, it is only recommended!
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
what we have been taught and what i have read from multiple publications..is..
in the event of any pressure drop during the 20mb phase of the tightness test all appliances must then be isolated and the carcas tested in isolation to establish if the carcas is leaking. Wether existing or new - no carcas pressure drops are permissable.
Indeed Only if it is found that the appliances are causing the pressure drop then do we fall back on the specified allowances Re permissable leakage/pressure drop based on meter type etc.
In essence thats what they state
I can post the screenshots from the publications ..
But my viper book doesnt go into as much detail lol
It might relate to new installs but I'm sure there's nothing in the IGE/UP/1b about shutting ISO valves on existing systems
Thanks for help kirky.
Is that email'abbabble !!
Thanks for help kirky.
Is that email'abbabble !!
Yes clearer thanks.
If you get a chance can you please send the page over leaf of the procedure.
Ta muchas :thumbup: