My boiler constantly bangs after its been shutdown for an hour or so..sometimes it's 5 or 6 getting shallower other times it's a few more 10 to 12.Its always after I've Ean the hot water on my potterton combi boiler. I live in uk and would love some help with this annoying issue.
Thanks.. Jon
 
Install a small expansion vessel on the mains supply to the boiler and close to it, some boiler manufacturers insist on this if they have preheat.
 
You said its always after DHW usage only?, you might narrow down the reason by switching off the boiler immediately after turning off the HW tap, then reopen the hot tap and run (cold) water through it for a few minutes then turn it off and see does the banging reoccur.
You may have a blocked plate heat exchanger.
 
Last edited:
  • Like
Reactions: jonkaw
You said its always after DHW usage only?, you might narrow down the reason by switching off the boiler immediately after turning off the HW tap, then reopen the hot tap and run (cold) water through it for a few minutes then turn it off and see does the banging reoccur.
You may have a blocked plate heat exchanger.
Sorry been away.Ran hot for a while then boiler off with hot tap running until cold plus a bit more. No banging. The system is still banging like I say after 90mins of running hot..very strange any more suggestions 🙏
 
Sorry been away.Ran hot for a while then boiler off with hot tap running until cold plus a bit more. No banging. The system is still banging like I say after 90mins of running hot..very strange any more suggestions 🙏

When you say no banging after running the water cold, did it still bang ~ 90 mins later or was DHW used again before this time had elapsed and then did its banging?
If it didn't bang after running the cold water through it then maybe worth installing a small E.vessel on the cold feed just before the boiler.
 
Gas valve not shutting off completely?

Some manufacturers claim this as: Parasitic Gas Valve.

Gas valve continues to pass gas when appliance should be shut down, causing flame to continue.
The boiler thinks the gas valve is shut, but the burner keeps going because their is gas available.

See if you can see if the burner is still alight when you turn the hot water tap off
 