Hi all our boiler has just had a new expansion vessel fitted but pressure is still going to 2.9 bars when using central heating . Is this normal? Than

View the thread, titled "Hi all our boiler has just had a new expansion vessel fitted but pressure is still going to 2.9 bars when using central heating . Is this normal? Than" which is posted in Boiler Advice Forum on UK Plumbers Forums.

Did the guy who fitted it not check it?

Filling loop left open?

There's something else that needs sorting then, had it twice last week.
 
Not normal, if sized correctly and with precharge&filling pressures of 1.0bar/1.5bar when cold, should not rise to more than 1.8/2.3 bar when hot.

If a external E.Vessel what size is it ?.

If a combi boiler might be a leaking HW heat exchanger causing mains water to pressurize the primary water side.
 
Not normal, if sized correctly and with precharge&filling pressures of 1.0bar/1.5bar when cold, should not rise to more than 1.8/2.3 bar when hot.

If a external E.Vessel what size is it ?.

If a combi boiler might be a leaking HW heat exchanger causing mains water to pressurize the primary water side.

Forgot about phe. If it's this then you will normally see an energetic needle on the pressure gauge when hot tap opened.
 
What make/model of boiler? Could be a blocked communication pipe to the vessel.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Hi all our boiler has just had a new expansion vessel fitted but pressure is still going to 2.9 bars when using central heating . Is this normal? Than" which is posted in Boiler Advice Forum on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
Sangita,
Last reply from
Deleted member 120897,
Replies
5
Views
2,285
Back
Top