Aug 2, 2023
Manchester
DIY or Homeowner
Jaga radiators (with heat-exchangers) have their own small fans, that "will modulate down when the room temperature is met – the room temperature is measured by a sensor at the base of the radiator", says Jaga. How does this coordinate with a standard room-thermostat, which of course shuts off the boiler-circulation when room-temp is reached? Should the rad's own sensor be set the same as the room-thermostat?
(I haven't got them yet, but considering two for the main knock-through living room, 2,200cu ft, running of a Vaillant condensing boiler, and using a low flow-temp setting.)
It’s not the room temp it turns the fan on when the flow into the fins is within limits and shuts off when it’s outside these
Eg turns on at 40 and goes off at 30 etc
I would use weather comp and fiddle with the curve until you have it right etc
Reactions: Mike K
Ok, good. Do they work well at low flow temps? (bit of a broad question...)
Oh dear, was worried about that... a noise etc website compared the 40db (of these rads) to 'the noise of a quiet library', but you're suggesting it's noisier than that..?
Well radiators don’t make a sound so it’s one of them in a bedroom I wouldn’t but where you have background noise you could probably get away with it
The only reason you would put Jaga convectors in with a fan would be in a area where a fanless unit would not provide enough heat.
In a bedroom scenario, put a unit in that is sized so it will not need a fan.