I did use my FGA, as I stated earlier, on the room test setting, with the casing off. This was because there was a piece of the rope seal that was missing and, on further inspection I had noticed that the rest of the seal had crumbled to dust, more or less.
As I don't want to be responsible for the demise of any person, for whatever cause, I decided to check for CO emissions and found that there was a considerable amount of CO being emitted from the area where the seal had deteriorated. I told the customer and, as previously stated, they were happy for me to switch off the gas supply and to get the seal replaced when I could.
The seal was subsequently replaced, the CO level was checked again, and there was no evidence of any CO leak following the replacement of the seal, so the boiler case was put can and I have now arranged with the customer to carry out a 'Proper' service in the next couple of days.
Aquazone - I thought that the level for a gas boiler was 0.0008, at least that's what I was taught anyway 🙂