been to a service on a ideal classic nf . sequence all normal all fires up lovely , then as expected when reaches temp, (burner flame out.fan off etc), then immediatly tryes to ignite pilot, sparks up pilot on for 1/2 seconds and then repeats this cycle till boiler drops in temperature then fires up as normal and repeats this over and over.

first thoughts replace pcb ,
but surely a board could not skip a range of safety checks ie fan aps stats etc to go directly to ignition .

any thoughs or suggestions appreciated.
 
the sequence at the start , confirms everthing as should be,
but when reaches temp. should really go to stanby until system cools and stat kicks back in. has me a wee bit baffled at the minute..
but it will attempt to ignite , and opens pilot valve for 1/2 seconds then off and then back on. and continues till stat takes over.,
 
I had a similar problem although not quite as odd recently, the fan would run for a second then turn off etc which was the potentiometer, but I would say board in your case as like you say something has to be a miss for it to skip through the sequence.

Does the APS close when the fan goes off?
 
would assume board checks aps for nc position , to confirm before activates fan, if aps was stuck .shouldnt go to next stage. boiler seems to have a mind of its own .
fan only starts after the stat kicks back in.
 
That's a strange one. Would say board, but never changed one and I look after a few of these. Normally very reliable, with the fan being the most common fault.
 

Official Sponsors of Plumbers Talk

Similar plumbing topics

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.