All the voltages are OK except those in colour. I'm not sure about the 90 volt readings, they could be a quirk of the valve, but the 225 volt reading on T7 at stage 5 is definitely wrong; it should be 0 volts.voltages taken today at each stage.[TABLE="width: 511"]
[TR]
[TD][/TD]
[TD]T 4[/TD]
[TD]T5[/TD]
[TD]T6[/TD]
[TD]T7[/TD]
[TD]T8[/TD]
[/TR]
[TR]
[TD][/TD]
[/TR]
[TR]
[TD]1[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]90[/TD]
[/TR]
[TR]
[/TR]
[TR]
[TD]2[/TD]
[TD]225[/TD]
[TD]0[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]90[/TD]
[/TR]
[TR]
[/TR]
[TR]
[TD]3[/TD]
[TD]225[/TD]
[TD]0[/TD]
[TD]225[/TD]
[TD]0[/TD]
[TD]225[/TD]
[/TR]
[TR]
[/TR]
[TR]
[TD]4[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]90[/TD]
[/TR]
[TR]
[/TR]
[TR]
[TD]5[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[/TR]
[TR]
[/TR]
[TR]
[TD]6[/TD]
[TD]225[/TD]
[TD]0[/TD]
[TD]225[/TD]
[TD]0[/TD]
[TD]225[/TD]
[/TR]
[TR]
[/TR]
[/TABLE]
Disconnect all wires from T7 and T8 except those to the cylinder stat
Turn stat to Minimum: You should get 0 on T7 and 225 on T8
Turn stat to Maximum: You should get 225 on T7 and 0 on T8
Check this several times. It might be worth checking to see if there is a point between max and min where you get 225v on both T7 and T8 - there shouldn't be one!
If you don't get the correct readings, the cylinder stat is faulty.