mid position valve faulty?

View the thread, titled "mid position valve faulty?" which is posted in UK Plumbers Forums on UK Plumbers Forums.

voltages taken today at each stage.[TABLE="width: 511"]
[TR]
[TD][/TD]
[TD]T 4[/TD]
[TD]T5[/TD]
[TD]T6[/TD]
[TD]T7[/TD]
[TD]T8[/TD]
[/TR]
[TR]
[TD][/TD]
[/TR]
[TR]
[TD]1[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]90[/TD]
[/TR]
[TR]
[/TR]
[TR]
[TD]2[/TD]
[TD]225[/TD]
[TD]0[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]90[/TD]
[/TR]
[TR]
[/TR]
[TR]
[TD]3[/TD]
[TD]225[/TD]
[TD]0[/TD]
[TD]225[/TD]
[TD]0[/TD]
[TD]225[/TD]
[/TR]
[TR]
[/TR]
[TR]
[TD]4[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]90[/TD]
[/TR]
[TR]
[/TR]
[TR]
[TD]5[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[TD]225[/TD]
[/TR]
[TR]
[/TR]
[TR]
[TD]6[/TD]
[TD]225[/TD]
[TD]0[/TD]
[TD]225[/TD]
[TD]0[/TD]
[TD]225[/TD]
[/TR]
[TR]
[/TR]
[/TABLE]
All the voltages are OK except those in colour. I'm not sure about the 90 volt readings, they could be a quirk of the valve, but the 225 volt reading on T7 at stage 5 is definitely wrong; it should be 0 volts.

Disconnect all wires from T7 and T8 except those to the cylinder stat

Turn stat to Minimum: You should get 0 on T7 and 225 on T8
Turn stat to Maximum: You should get 225 on T7 and 0 on T8

Check this several times. It might be worth checking to see if there is a point between max and min where you get 225v on both T7 and T8 - there shouldn't be one!

If you don't get the correct readings, the cylinder stat is faulty.
 
All the voltages are OK except those in colour. I'm not sure about the 90 volt readings, they could be a quirk of the valve, but the 225 volt reading on T7 at stage 5 is definitely wrong; it should be 0 volts.

Disconnect all wires from T7 and T8 except those to the cylinder stat

Turn stat to Minimum: You should get 0 on T7 and 225 on T8
Turn stat to Maximum: You should get 225 on T7 and 0 on T8

Check this several times. It might be worth checking to see if there is a point between max and min where you get 225v on both T7 and T8 - there shouldn't be one!

If you don't get the correct readings, the cylinder stat is faulty.

Have done what you said.
at minimum T7 60v T8 225v
at maximum T7 225v T8 60v
there is no point where both T7 and T8 are at 225v
the change over happens at the point of tank temperature which at the moment is 60° and an audible click of the stat is heard
Where's this 60v reading come from?
 
Then the cylinder stat is knackered!

OK, I will get a new one. I will check when I wire it in if I get this 60v.
The whole kit(stats,prog,valve)is an Iflo (specific to Travis Perkins?). Would you replace like for like or go with another brand. The Iflo look like a Drayton clone or it could be the other way round.

Many thanks for your invaluable help

mick.
 
Iflo is made for Travis Perkins by Drayton, but that does not mean they are made to the same standard.

It's OK to mix kit; I prefer Honeywell kit as it seems to last longer.

Check for the 60V when only the common is connected.

The terminal numbers are the same for the Drayton/Iflo and the Honeywell L641A.
 
Last edited:
Iflo is made for Travis Perkins by Drayton, but that does not mean they are made to the same standard.

It's OK to mix kit; I prefer Honeywell kit as it seems to last longer.

Check for the 60V when only the common is connected.

The terminal numbers are the same for the Drayton/Iflo and the Honeywell L641A.

Fitted a new Drayton cylinder stat today. Before attaching wiring to T7 and T8, yellow wire from stat to T8 was 225v, blue wire from stat was 0v
Will see how it goes.
 
Fitted a new Drayton cylinder stat today. Before attaching wiring to T7 and T8, yellow wire from stat to T8 was 225v, blue wire from stat was 0v
Will see how it goes.

The new cylinder stat has not fixed the problem. Boiler would not switch off again today. Took valve head off and gave it a shake, the lever then moved from the mid position to CH and the boiler turned off as it should.
Will be getting a new head on Monday.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "mid position valve faulty?" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
drollord,
Last reply from
drollord,
Replies
34
Views
12,254
Back
Top