Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Oct 9, 2018
9
0
1
North east
Member Type
DIY or Homeowner
Hi guys please be nice I'm not in the trade ☺️

Fitted two rads yesterday to an existing system one to replace an old one and another one totally new and extended the rad circuit. The issue I have is they warm up perfectly but after about an hour or so one goes cold. The rad isn't the last in last in circuit the other new one comes after it. I've used this rad Kudox Premium Type 21 Double-Panel Plus Single Convector Radiator 600 x 1200mm White with this Drayton RT212 White / Chrome TRV & Lockshield 15mm x ½".
Does the trv have a built in thermostat which is cutting the feed as the room has hit temperature? There is no other room thermostat. I'm thinking this is the issue but was hoping someone could confirm this.

Cheers Andy
 
Which to a uneducated person is? All the pipe on existing rads in the house is 10mm or is it the fact I've joined another rad to one with which is 10mm i take it should be from a bigger pipe somewhere?
 
Thanks guys and sorry.. So basically find the manifold and connect the new directly to that so the rads aren't sharing the feed and then the rads will get the heat benefit. One last question from what you can see it's not dangerous atm or what I have done could it damage the boiler? Really sorry to bother you guys I really wouldn't ask but if I could afford to get someone I wouldn't have done this.
 
Should be alright though if you balance the system?
You might also have an air lock in that leg. If it’s on s drop down. Feel the glow pipe running wall. If it’s only hot at the top, it’s an air lock.
Turn all other rads off to get it going, then balance the system.
 
  • Disagree
Reactions: Riley
Hi again guys funny thing is it cloudve been the trv or balancing. I've done some adjustment to both and the radiator is staying on all the time now and every radiator is running red hot. When looking at the balancing around the house every lockshield was fully open so I'm guessing these rads had no chance really. I really do appreciate the time and effort you his took in trying to help me out I really appreciate it
 

Official Sponsors of Plumbers Talk

Similar plumbing topics

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.