Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

MarkAqua

Plumbers Arms member
Plumber
Gas Engineer
May 20, 2010
448
170
43
Not too clued up on domestic control systems, so was wanting a bit of advice,

Potterton EP2001 programmer, CH & HW
MID postion valve
Honeywell T6360 room stat

I've got no power coming into their room stat
The geezer has replaced the stat but didn't make a difference. Hence calling me.

Hot water works fine,
I've belled the wires from stat to wiring center and all have continuity.

Can't seem to get a voltage reading out of the top of programmer when Heating is on and it is coming up with random lines on the display.
Oh and the custard put a link between white and orange wires for mid position valve and heating worked constant (no control on thermostat)

I'll attach pictures

I am thinking it's the programmer at fault as I've checked the wiring and terminals and all is good everywhere.

Cheers for help lads

IMG_4437.JPG
 

Official Sponsors of Plumbers Talk

Similar plumbing topics

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.