I have a unvented system and have run a secondary return on the hot water due to the size of the property. I have a non return valve directly after the bronze pump that rattles and is causing a nuisance. Is there a diff type of double check valve i can use to stop this rattling?
 
I normally use this type.
But it must be installed in the horizontal or with the arrow pouting up.
 

Attachments

  • ae235.jpg
    ae235.jpg
    17.9 KB · Views: 51
  • Brass-Horizontal-Check-Valve-CN404.jpg
    Brass-Horizontal-Check-Valve-CN404.jpg
    16.4 KB · Views: 56
Last edited:
Those check valves always rattle, the swing valve above will remedy it & prolong pump life probably
 
  • Like
Reactions: 1 person
ive found sometimes that no returnes can be noisy when there the spring type and they've jumped out of place, try replacing the valve like for like first or as above use the swing valve
 
fbd570bd29da76435fbe174eb2b55476.jpg


I've installed a double check valve. Have no idea if it's spring loaded or no? Maybe I'll try and like for like swap and see what happens. I've never heard of the swing valve before?
 
Ok I'll pick one up tomorrow from pipe centre. Any reason why it has to be installed horizontal? My NRV currently points down after my pump then into my megaflo.
 
But the pressure of the unvented cylinder will surely close it? It's basically another hot water outlet on the cylinder. I thought the NRV was to protect the pump?
 
But the pressure of the unvented cylinder will surely close it? It's basically another hot water outlet on the cylinder. I thought the NRV was to protect the pump?

Think about it Dan what pressure is there at the other end of the return away from the pump?

So long as the hot & cold are all balanced & the pump is running when any hot water drawn, then I am not convinced that a non-return is required but the MI's alway show. It is installed to stop cold water from the feed being drawn back up the return to the taps missing out the cylinder as it were.

When no water is being drawn then both sides of the check are at the same pressure but flow from the pump will push the gate open so water can circulate around the closed circuit.
 