I've cut the other bits but from IGE/UP/1B on testing existing installations
Quote
h) Check for any pressure drop over the next 2 minute period.
If the pressure drop over this period does not exceed the value given in
Table 1 and there is no smell of gas, the installation shall be deemed to have
passed the test.
If the pressure drop exceeds the value given in Table 1, or there is a smell of
gas, the installation shall be deemed to have failed the test.
i) Where no appliance is connected, there shall be no perceptible movement
(fall) on the gauge reading over the 2 minute test period and there shall be
no smell of gas. If there is no perceptible movement of the gauge reading
(see clause 4.2.2) and there is no smell of gas, the installation shall be
deemed to have passed the test.
No mention of then isolate and find it but you should use your judgement and common sense.
Tam you are the man, cause you said the same as me, obviuosly, we need to discuss the reg NOT our wishes as they are not the same, as a lot of us go above the reg as is our perogative/agreement with the paying customer