M mgrover Oct 30, 2023 #1 bit of an odd one. UFH been working fine for about a year or two now. today the pipes going to it before the zone valve are stone cold. its a very basic system with Hive thermostatic valves controlling the rads upstairs and the zone valve downstairs. Could the pipe be blocked?
bit of an odd one. UFH been working fine for about a year or two now. today the pipes going to it before the zone valve are stone cold. its a very basic system with Hive thermostatic valves controlling the rads upstairs and the zone valve downstairs. Could the pipe be blocked?
M mgrover Oct 30, 2023 #2 Ah nevermind figured it out. Basically the zone valve had got stuck shut. Its a honeywell one shock horror. Anyways I force it into the open position and everything went back to working. Put it back to the normal position and so far so good.
Ah nevermind figured it out. Basically the zone valve had got stuck shut. Its a honeywell one shock horror. Anyways I force it into the open position and everything went back to working. Put it back to the normal position and so far so good.
M mgrover Oct 31, 2023 #3 ended up replacing the synchro motor on it. bit odd its died tbh given its only been around a year and a half. but that is from a lot of running every 2 hours finally had loft insulation and cavity wall insulation installed today. Last edited: Oct 31, 2023
ended up replacing the synchro motor on it. bit odd its died tbh given its only been around a year and a half. but that is from a lot of running every 2 hours finally had loft insulation and cavity wall insulation installed today.