New to this forum so I will try especially hard to be succinct. It would be so helpful to have some feedback and see if I'm anywhere close to a solution or still miles off the mark.

I am completely refurbishing a bungalow I have bought, all internal walls down, new rooms in different positions. The floor is an uninsulated groundbearing concrete slab (approx 100-150mm). I plan to run a new soil pipe under the floor, with the highest level of the 'horizontal' pipe being no higher than the underside of the slab. This new soil pipe will follow the line of the existing (removed) soil pipe but at a lower level. Please see the attached sketch, this seems like the simplest way of doing it but I am eager to get some feedback as it will almost certainly need some changes. I have two questions in particular, but welcome all constructive thoughts.

1) Being on the ground floor, without any vertical drop to help speed waste along, do I need a steeper gradient? I have currently done my workings based on 1:80, which I understood to be correct by the building regs based on anticipated peak flow and pipe size (110mm).

2) Downstream from the WC I need to connect a washbasin, shower, kitchen sink/dishwasher. My natural instinct was to use a strap/boss/adaptor (each solvent weld), however I wanted to be sure that this is suitable for a) a horizontal run, and b) underground use.

Any comments on the above and one the design in general would be much appreciated 🙂

Kind regards,

Chris
 

Attachments

Thanks SimonG, ShaunCorbs & king of pipes for your replies.

I have started a conversation with building control about what I intend to do, so hopefully they will give me some advice soon. I don't know if they are doing visits currently?

The boss pipe connectors look good, do I need to be careful solvent welding to brown pipe or is it all the same material? I'm sure this is a classic plumbing forum question! I have read somewhere that they are not suitable for exposure to UV which makes sense, or are they brown just as a sensible colour-code?

Cheers,

Chris
 
Not getting involved with underground pipe jointing methods - we only used glued fittings.

There is no vent in the system.
You will need a vent - preferably as close as to the furthest upstream fixture.
Not an AAV, but a vent to atmosphere.

Hope this helps
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Plumbing design in bungalow refurbishment" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

Joined
Member Type
DIY or Homeowner

Thread Information

Title
Plumbing design in bungalow refurbishment
Prefix
N/A
Forum
UK Plumbers Forums
Start date
Last reply date
Replies
7
Unsolved
--

Thread Tags

Tags Tags
None

Thread statistics

Created
chrisjmet,
Last reply from
oz-plumber,
Replies
7
Views
2,566

Weekly or Monthly Email Digest

Back
Top