Plume kit to move from a window?
View the thread, titled "Plume kit to move from a window?" which is posted in UK Plumbers Forums on UK Plumbers Forums.
C
Chrisgy
Got a boiler to fit tomorrow. The flue will be 150mm from openable window, so the surveyor has said to fit a plume kit to take it away from window. Is this allowed? It's a Worcester going in
No its not allowed , minimum 300mm from an opening to a building and you cannot use a plume kit to extend it
why ,thought that is what a plume kit was for ,to take fumes away from places like conservatorys with openable windows otherwise what they for ?
someone posted a link on here to a worcester mi not so long ago saying you can do this
This is ringing bells with me, I think that it allows the flue tobe 150mm closer DO NOT QUOTE ME ON THAT though, I see if I can find a link.
EDit look at the link that Bronzino has posted,, WB says it can be done.
flue can come out of the wall and be less then 300mm to window,they and vailant allow it cos i have spoken to there tech services !!
you HAVE TO USE PLUME KIT TAKE PRODUCT OF COMBUSTION AWAY ! and it all make sense to you ones you open your boiler and have look on that separate book for FLUE TERMINALS that comes with it!
though you as gsr will know this !!!
the reason ive put this answer is ,my mate fitted a plume kit for this very reason cos the boiler could go nowere else in the house and the only way was with plume kit cos was near a window on next doors conservartory and he is gsr so i thought its ok
Did you already know this then when you rang their tech services. No need to HIGHLIGHT PRODUCTS OF COMBUSTION and FLUE TERMINALS I do understand. Obviously this is something certain manufacturers allow and it looks like Worcester is one of them.
yes cos I did days training with them,but I also was told about FLUES and FLUE TERMINALS in my training centre !!
Sorry if I was a bit .......I am taking it back !!!No bad thoughts here .
The plume management kit is not a standard flue. It is to aid in the removal of plume away from areas that the plume may still cause a nuisance when the standard flue is fitted to MI's/regs.
It cannot be used to make an illegally fitted flue become compliant with the regs/MI's.
"It cannot be used to make an illegally fitted flue become compliant with the regs/MI's"
how do you mean ?
can you explain ,pls!
Say the MI's state min. 300mm from opening window. You cannot install a boiler with its flue fitted 150mm from opening window and then stick on a plume kit to attempt to bring it into line with the MI's. The boiler with its standard flue is installed not to MI's.
It is called a "plume kit" it is to take away any nuisance plume. It is not a flue extension kit.
off the top of my head I am sure worcester say if a plaume management kit is usedthen distance from openable window can be reduced to 150mm
i agree with the above...it is allowed.
I would need to see this in writing then.
If I come across any WB flues as close as 150mm to an opening window with a plume kit, when the MI's state min. 300mm I will still be 'AR' it.
If you fit a plume kit then the terminal that discharges the POC's is going to be a greater distance than 300mm to an openable window. It is only the air intake on the flue that will still be 150mm, so no problem.
It turned out to be an ideal logic this morning so I rang ideal and they said that's not a problem
Gasman would perhaps be the man to answer this. He fits them.
You could always ask Baxi themselves.
applies to baxi and potterton aswell. air inlet can be 150mm from opening using plume kit
can be used exactly the same, can fit 150mm from a corner but must end up terminating 300mm from the corner
can agree with this went on a course at worcester and this was the first question i asked, and they confirmed the above, it is allowed to be reduced by 150mm aslong as the plume kit is over 300away, my other question was about allowing the white section of the flue to be exsposed to allow the flue to exstend past the eaves of a roof, as we had a inspector say its not allowed, but this is also allowed as long as joints of flue are sealed with a sealant and also states you can paint the flue to protect it, its now in the mi for worcesters and baxi's havnt checked many other boilers but alot of things people think are not allowed are allowed,, worcester told me they do seperate investigations into things and then bring out update notes etc if they prove something to be safe, but these often only apply to there boilers!
Reply to the thread, titled "Plume kit to move from a window?" which is posted in UK Plumbers Forums on Plumbers Forums.
Chrisgy,
SafeGasInstall,
