Steve weightman

Gas Engineer
Jan 4, 2019
185
78
28
Member Type
Heating Engineer (Has GSR)
Has anyone experienced a boiler with pulsating flames in a combustion chamber I've serviced a baxi megaflow system boiler today with the analyser readings saying wtf and could hear the irregular flame noise.
Thanks
 
Fan sealing poss, had that on an old W.B. 26 cdi extra for my sins.
One of the old boys had a chuckle & told me about needing perfect sealing which is not easy to see sometimes,
Cheers,
Andy
 
What were the min & max CO2 readings? And did you fill the condense trap back up after you cleaned it out?
 
if its pulsing sounds like its hunting for air so maybe over gassed whats bp / gas rate?

/ have you checked your flue integrity
Hi the inlet pressure being 21mb but the burner pressure is bouncing and the flue is fine . Thanks
 
@Steve weightman I sound the gas valve needs setting up. It should have the same gas valve as a 24i junior.
Hi the gas valve was buzzing big time so got it down to a dodgy valve . Had a job with new one it's settings was way out my fga locked out instantly i expected to set it up but not to the extent the burner was blowing out
 