So if it's heating up the room at a rate of between 2.5C - 3.0C / hour, this is too slow? I think it's too slow, but wondering what opinions are.
This is with heating system at ~60C at the boiler, and the thermostatic valve radiator turned up full.
Having used several online calculators the highest BTU I get on any calculator is 3788 BTU using: Radiator Sizing Calculator - BTU and KW - http://www.radcalcer.co.uk/ for the room.rad sounds undersized
It's a WB Combi 30i boiler with the rad below:You say you have a flow temperature of 60°c? Is this a condensing boiler.
I have pointed a contact free thermometer pointed very close to the rad and it gives a temp of ~58 C.From -10 to 21dc 14 mins so something isn’t right
does the rad get hot hot eg 60dc ish
Thanks.I would say the specs that the manufacturer has claimed are over zealous and would estimate it to emit around 1.5-1.8 kw (max)as it’s basically a single panel rad
Unfortunately I don't have a plumbing background, so I'm unsure what exactly this means.
I understand that k2 is a type of rad. Do you mean if using a double panel 1.2m x 600mm K2 rad this would give an average BTU output of 7401 BTU?
The current rad type which I have would probably need to be a lot bigger to heat up the room in 30 minutes since it's heating the room at ~ 2.5C - 3.0C / hour.
So essentially if I wanted to get this make/model of rad to heat the room up in a reasonable amount of time (and I only wanted one rad as it's a small room) the rad may need to be in the region of twice the output size of the one currently installed?correct
or another rad installed in the same room eg two rads
Also because you are running with a boiler temp of 60C then you will only be getting ~ 65% of a 50 deg rad output or ~ 4810 BTU (1.4kw).So essentially if I wanted to get this make/model of rad to heat the room up in a reasonable amount of time (and I only wanted one rad as it's a small room) the rad may need to be in the region of twice the output size of the one currently installed?
Should the boiler temp be run at a different temperature? I've set the WB combi to the recommended "e" setting and this is usually about 60C.Also because you are running with a boiler temp of 60C then you will only be getting ~ 65% of a 50 deg rad output or ~ 4810 BTU (1.4kw).
If you increased the boiler temp to 75C and with a radiator deltaT of 15C, you would then almost have a 50 deg (47.5) rad again or 94%% output but the boiler is then running with a return temp of 60C which is very uneconomic, if you run with a delta T of 20c you are down to 87% output, all rads should really IMO be oversized by a factor of at least 1.5 to allow for condensing boilers which run most efficiently with return temperatures of 50C or less.It looks like their only larger rad of this style is:
which has 9163 BTU as opposed to the 8218 BTU for the one which I have. I'd guess this won't make a huge difference in getting the room warmed in 30 minutes, so perhaps I might look at some other radiator design.![]()
1800 x 560mm White Vertical Traditional 3 Column Radiator
Create an old fashioned traditional look with these vertical column radiators, 1800 x 560mm and triple layered for extra warmth.www.radiatoroutlet.co.uk
Apparently, with regards to the vertical rad which I have, there is no specific flow/return and it can be installed either way.This site has numerous posts re problems with vertical rads, some have to be installed in a certain way as they have a baffle to get the water circulating properly and apparently sometimes this isn't pointed out in the installation instructions. I would suggest taking numerous temperature readings on the columns and make a little sketch with the temps noted on it, as a very quick check you might just measure the temperatures at the flow and return connections, if these are only a few degrees apart then IMO you have a problem, just feeling the rad all over even should tell a lot.
I suppose there are two calculations that the heating engineer should do when sizing radiators, one is the calculation for the heat loss and the other for the correction factor to apply to a 50 deg rad. A required return temp of 40C with deltaT of 20C will result in a 30 deg rad based on a required room temp of 20C or a 27 deg rad based on a more realistic required temp of 23C, this will result respectively in 51.5% output and a correction factor of 1.94 or 44.9% output with a correction factor of 2.22, so as suggested with the above slow warm up problem, maybe install another rad of the same size?. It would be interesting if the flow and return temps were actually measured in the above case as the "58C" measurement implies a delta T of 4C (boiler temp 60C) which is unlikely IMO.
With regards to the point above, the valve retailer states that they, "recommend installing the wheel head on the flow in and the lock-shield on the return."The TRV is installed on the return, ensure it is bi directional (arrows pointing both ways), I would open it fully, remove the head and using the shaft of a a reversed hammer press the actuating pin firmly in, it should spring out but the movement is only ~ 5MM,
It's a steel radiator, just in the style of a traditional column rad.Heat up time of 20 minutes seems very long but again if these are cast iron maybe normal, I'm sure some one on here can advise,
Practically speaking my only suggestion is to get hold of a oil filled rad or equivalent, turn off the rad, set the electric heater to whatever power settings are available and that should point you in the right direction. My oil filled rad has three settings, 0.8kw(2730BTU), 1.2kw(4094BTU) and 2kw(6824BTU)