Has anyone got a good rule of thumb for sizing an expansion vessel for a central heating system. A combi has a 8 litre vessel. And will deal with the expansion of say 8-10 rads. Could one use this as a ball park figure and multiply up from there Obviously pipe work to take in to account 22mm or if any 28mm on the system. Thanks for any input
 
Did/can you confirm that the pressure was 2 bar with boiler/circ pump off? This is important.

That gives a system contents of 720 Litres

1642024023334.png
 
The 66/55C flow/return will only be valid if the boiler was running constantly, ie a gas boiler, if not, or an oil boiler which always cycles then the system dT and the boiler dT will be completely different.
 
Thanks the boiler is pretty much running constantly there is huge heat loss as one wall of the whole building is nearly completely glass. Sorry I would have to check the pressure when the pump is off. This is seen as the true pressure?
 
Yes, it will give the true reading then.
If all the readings are correct, the spreadsheet will be correct, 720 litres seems a huge systems content though,
the exact pre charge pressure also has a huge influence on the results, for example if it was 1.25 bar (or 0.5bar) the system contents will be 540 Litres.
One way or the other though. I think you should be quite confident that a 50 litre EV will have no problem in dealing with the extra rads water content.
 