I would have to check this as again it is behind kitchen units and blocked in but I am sure I could see something behind one of the drilled holes for the stopcock... whatever happened to easy access to pipes 🙄
If you cant see the vertical pipe near the dishwasher then look for something like this under the sink. With a Grey ribbed hose on the small side nozzle, hopefully with a metal clip keeping it in place. 🙂
Sink Trap with 135° Swivel Nozzle
 
Any chance of a pic of the sink and underneath eg pipework in the utility room ?

I can get a pic of what I can see ie directly under the sink but there are a lot of pipes behind the kitchen/utility unit carcasses which without cutting them out cant be seen/accessed - Is this the new way of fitting out houses - block all the plumbing in!!! Same in my bathroom where I also had a leak through the ceiling, I have had to disrupt floor tiles and the whole of the side of the bath was tiled with no access to the pipes so have had to disrupt all the lovely mosaic tiling too - Grrrr .....
 
I can get a pic of what I can see ie directly under the sink but there are a lot of pipes behind the kitchen/utility unit carcasses which without cutting them out cant be seen/accessed - Is this the new way of fitting out houses - block all the plumbing in!!! Same in my bathroom where I also had a leak through the ceiling, I have had to disrupt floor tiles and the whole of the side of the bath was tiled with no access to the pipes so have had to disrupt all the lovely mosaic tiling too - Grrrr ...

That's fine ta

Sometimes yes (some people don't like to see pipes)
 
Is this the new way of fitting out houses - block all the plumbing in!!! Same in my bathroom where I also had a leak through the ceiling, I have had to disrupt floor tiles and the whole of the side of the bath was tiled with no access to the pipes so have had to disrupt all the lovely mosaic tiling too - Grrrr ...

Grrrr indeed, welcome to our world 😉
 
  • Agree
Reactions: Ric2013
I am going to try and upload the photos now.... Hopefully you remember our comments above....the white pipes are the under the sink where the dishwasher is in the next cupboard and the grey pipes are in the utility room where the terrible smells are coming from.... also the soil pipe run up through the utility room to the upstairs toilet.....

20170922_162820.jpg


20170922_162828.jpg


20170922_162844.jpg


20170922_163017.jpg


20170922_163038.jpg


20170922_163105.jpg


20170922_163113.jpg


20170922_163119.jpg


20170922_163123.jpg
 
Is this house Detatched, Semi, Terrace, or flat?

If it's semi , terrace or flat it may not be your drains causing the smell.
In fact it may not be drains at all.

Try pouring something with a strong odour, like mouthwash or Jeyes fluid or bleach (a whole bottle not just a drop), down the kitchen sink waste.

If the smell comes out in the affected rooms it confirms it's an open drain venting to inside. If it does you may be able to pin it down to a room.
 
  • Agree
Reactions: keira01
My three penneth.

Issue is no vent to atmosphere for the soil stack...

Builders etc fit AAVs but do not understand the dual role of a soil stack. Suspect malodour coming back up or traps being sucked dry when something like WC being flushed causing odours to be smelt.

Action is to find the AAV, remove it and extend pipework so foul smells can be vented. The vent needs to be a min of 50mm but pref 4". Outside it must terminate at least 900mm above last opening window if within a certain distance - bugger cant remember!
 
  • Like
Reactions: Stigster
My three penneth.

Issue is no vent to atmosphere for the soil stack...

Builders etc fit AAVs but do not understand the dual role of a soil stack. Suspect malodour coming back up or traps being sucked dry when something like WC being flushed causing odours to be smelt.

Action is to find the AAV, remove it and extend pipework so foul smells can be vented. The vent needs to be a min of 50mm but pref 4". Outside it must terminate at least 900mm above last opening window if within a certain distance - bugger cant remember!

Hi thank you for your reply. My plumber was of the same thoughts as you so he has extended part of the soil pipe (there was an easily accessible branch downstairs to which has has added an extension to the outside and upwards in the hope that this would solve the problem (by venting out this way) without having to break into all my plastered walls to find the top of the soil pipe (as its not in the loft and no obvious evidence elsewhere so has to be in the walls?) So for 4 days there was no smell and today it has started again. I am back at the beginning again now. Would you suggest now finding the end of the soil pipe (by breaking into the walls) and capping it off at that point so it has to go out of the extended part he has just put in?? Or could it be something else? Its a massive nuisance.
 
On photograph 4, the convoluted grey pipe appears to be wet. Also there is evidence of corrosion on the compression fittings. Where is this water coming from?

What do the smells smell like? For example, are they 'mushroomy' (fungus or rotting wood), 'eggy' (hydrogen sulphide) , rotting vegatables (mercaptans), etc. ?
 
what size pipe has been used to vent? it needs to be 2" (50mm) minimum. 40mm will NOT suffice.
PLUS you should fit anti vac traps to basins & sinks.
why? because its quite likely that a trap is having its seal sucked out. if you fit anti vacs everywhere you can it helps reduce that impact by allowing more air into the system.
 
  • Agree
Reactions: keira01
what size pipe has been used to vent? it needs to be 2" (50mm) minimum. 40mm will NOT suffice.
PLUS you should fit anti vac traps to basins & sinks.
why? because its quite likely that a trap is having its seal sucked out. if you fit anti vacs everywhere you can it helps reduce that impact by allowing more air into the system.
I don't know about pipe size on the extended bit I will have to find out but it is the same size as the soil pipe (I think) - Is it possible this isn't working because the end of the soil pipe still has an AAV (behind walls as stated above) on it that is possibly malfunctioning? or should the extended pipe pull the gases/smells through to the outside . Thanks for all your advice.
 
On photograph 4, the convoluted grey pipe appears to be wet. Also there is evidence of corrosion on the compression fittings. Where is this water coming from?

What do the smells smell like? For example, are they 'mushroomy' (fungus or rotting wood), 'eggy' (hydrogen sulphide) , rotting vegatables (mercaptans), etc. ?
I think eggy..... (although not sure exactly what others smell like)....
 
with an adequate vent the aav's condition will not impact performance. However, if its failed open it WILL stink the place out. in your shoes id find it and either cap it off or extend it to vent as it should have
 
Ok... I guess its not failed open as the smell isn't always there.... it mainly appears in the area of the soil pipe downstairs once the loos and sinks (upstairs) have been used and flushed in the morning and then it is not every day it happens - it can go a few days with nothing and then the last two days it has happened each morning. I have two issues - traps and soil pipe I think.... The plumber also told me that the soil pipe has a few bends in it to get to the eventual ground extraction point (which he advised should not be happening on a soil pipe!!).... its a DIY botch job I think and everything is behind walls, kitchen units etc to give me maximum disruption to sort it all out.
 