He is trying his best but I have retained some money until it is resolvedOh dear ... what does your builder say about the matter . he was the main contractor
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
He is trying his best but I have retained some money until it is resolvedOh dear ... what does your builder say about the matter . he was the main contractor
He is trying his best but I have retained some money until it is resolved
Yes I have his name and number but I’m leaving it up to the builder to sort out, if I have to get another engineer out then the retained money won’t be paidGood man ... the wallet always hurts .. don’t you know the name of the plumber?
Yes I have his name and number but I’m leaving it up to the builder to sort out, if I have to get another engineer out then the retained money won’t be paid
Thanks Craig finally someone gets my problem lolThe blending valve should have a range of around 35 - 65 ° so if you can't regulate the temp down then there may be an installation issue or a fault with the blending valve. Ask your contractor to contact the manufacturer of the underfloor heating to get a rep out to check the system over.
😉Thanks Craig finally someone gets my problem lol
I am still at a loss what are you saying that the mixing valve is not capable of controlling the water temp in the U/F circuits as 45-50dec C when the boiler thermostat is set to provide 70 degC ?problem one is we have to slowly build up the heat as the new floor is tiled but the only way to do this is by turning the boiler heating controls down as low as it goes, 30 degrees, if we have it set to 60 the temp on the flow is 45 degrees which is the maximum we can run at.
Chris you are asking questions that im not sure I can answer, I’m by no means an expert on ufh but my tiles cost an awful lot so I know not to thermal shock them, I can’t find another way of explaining the issue other than what I have already posted, tiled screeded floor maximum temp is 45 degrees at manifold, when ufh is switched on you must progress to this temp gradually, I can’t do this without setting my boiler to minimum which in turn knocks out my radiators, the blending valve should allow me to do this but I can’t?I am still at a loss what are you saying that the mixing valve is not capable of controlling the water temp in the U/F circuits as 45-50dec C when the boiler thermostat is set to provide 70 degC ?
It is the surface temp of the tiles finish which is more important than the mean water temp, as from your posted you can see the water temp can be higher although I personally would limit it to 60. Who selected the rads ? what delta T was used ? ie. what is the design system operating mean water temperature?
Thank you for another angle on this bogrodder, I have purchased a temperature sensor gun to test the temperature gauges and tile temperature so will get a better idea once it arrivesBlending valves and the associated thermometers attached are never accurate, I know this from lots of testing with calibrated equipment. They can be far out as much as 10 degrees. Get somebody decent in to check things over.
I’m not sure on how well that would work but thanks for the idea, we have managed to get the UFH guy back and he has agreed it looks like the blending/ mixing valve that’s at fault, I’ll update when the new valve is fitted!cant you turn the boiler temp up and turn the flow rate down to lower the temperature to each circuit