Where you are short of heat output, you can go under the units. But it's best not to, especially where you want to store food.
 
If you're remodelling the kitchen then simply adhere some kingspan or similar product underneath the cabinets & fit some vents to the plinths to allow the heat to circulate into the room, If you're installing the UFH then why waste time, energy & money on extra meters of pipework etc. that's really unnecessary, & will give no benefit to the end user at all just heating a dead space.
 
Hi there,

when we design the system we never go for UFH under the kitchen units (as long as we know exactly where kitchen units will be).
In some cases when customers haven't got a final design of the kitchen they cover the whole area with pipework and then they use thin layer of insulation board underneath the cabinets.

Hope that helps.
 
Hi there,

when we design the system we never go for UFH under the kitchen units (as long as we know exactly where kitchen units will be).
In some cases when customers haven't got a final design of the kitchen they cover the whole area with pipework and then they use thin layer of insulation board underneath the cabinets.

Hope that helps.

Can you please explain why? (apart from the cost)

I thought that these system were more of less self regulating i.e. as the air temperature increases the heat flow from the thermal mass of the floor decreases.

If there is no heating of the thermal mass under sections of the floor isn't heat drawn away from those areas that are, reducing warm up time & possible effecting overall heat outputs?

Thanks Chris
 
Last edited:
Hi Chris,

Running the pipes under the kitchen units doesn't cause any problems as long as there's no food being stored in the kitchen units.

This is the main reason why most of companies don't recommend to install the UFH underneath the units.

I agree with the fact that colder screed will suck the heat from the warmer areas but's it's only for the initial heating up times.
If there's plenty of units within the kitchen we normally narrow the pipe spacing to 150mm which reduce the response time to provide a bit more output.

Regards
 
Just had a look at your Web site 32mm pipe haven't seen that before!!

That might come in handy for some of the larger jobs, what sort of heat loads can it supply at say 70/50?
 
Morning Chris,

32mm pipe is being used for general plumbing together with press or compression fittings.
We've never supplied 32mm pipe for the UFH, even for commercial jobs we've done 20mm pipe @ 300mm / 200mm centres depends on the project requirements.
I haven't even got any figures with outputs of 32mm pipe to give you honest answer.

Have a good day.
 
Morning Chris,

32mm pipe is being used for general plumbing together with press or compression fittings.
We've never supplied 32mm pipe for the UFH, even for commercial jobs we've done 20mm pipe @ 300mm / 200mm centres depends on the project requirements.
I haven't even got any figures with outputs of 32mm pipe to give you honest answer.

Have a good day.

I was thinking more about the distribution to manifolds etc rather than U/F circuits themselves, still handy to know.

Thanks anyway Chris
 
I have underfloor heating under a large kitchen island. I put the kitchen on chromed feet (no plinths) and the heat dissipates easily. The floor barely gets warm but heats the whole room. The only place you can feel a small measure of heat build up is under the dogs memory foam bed.
 
Good morning Chris Watkins and ShaunCorbs,

I'm sorry about the delay but the top man in technical @ Factory was away for a while.

Here's some details about 32m pipe and how much heat can it carry:

Temp. 90/70 80/60 70/50 70/55 60/50 55/45
d32x3 32000W 31000W 31000W 23000W 15000W 15000W

Hope that helps.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "ufh under kitchen unit" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

snoopy8888

Gas Engineer
Joined

Thread Information

Title
ufh under kitchen unit
Prefix
N/A
Forum
UK Plumbers Forums
Start date
Last reply date
Replies
14

Thread Tags

Tags Tags
kitchen

Thread statistics

Created
snoopy8888,
Last reply from
Uheat – Wojtek,
Replies
14
Views
9,900

Weekly or Monthly Email Digest

Back
Top