Hello,

we have a Vaillant EcoTec Plus 938 boiler and it started behaving when running in heating mode (hot water is fine - no problems with that).

The problem is that quite often when there is demand for heat (either from one of Hive TRVs or from under floor heating thermostat) boiler starts up but feed water temperature stays below 40 degrees (typically 35-38). Pump seems to be running, burner is on at minimum level. Sporadically it can go up to 60 for a short period of time then back to 40. Sometime however it works fine. What could be the issue? I'm suspecting low water flow rate, but I have no way to check this. Looked at diagnostics menu on the boiler and it doesn't seem to have water flow displayed in there.

Appreciate any help with diagnosing this issue.

Thanks,
Sergey
 
This boiler even with a big call for CH Iwhere the bypass would/should be shut in any case if installed only occasionally gets up to 60C so maybe some other problem. One of the main reasons for a external bypass is to dissipate some heat with boiler shutdown and pump overrun, another is to keep the flow/return < Say 30C with very low circulation flows. Some boilers, probably with SS HXs don't require them. ABVs don,t work with modulating circ pumps IN PP mode and need very careful adjustment with pump in CP mode hence the recommendation above for a manual bypass.
 
Internal bypass is fine, you won't need an external one. That's what it's there for.

I'd set your pump to 100% on d.014 and it maybe that you bypass wants adjusting internally on the boiler, which your plumber will need to do.

And put Partial load back to Auto.
Thanks a lot! Looks like this solved the issue - added 1 full turn on the internal bypass, set output to Auto and now it goes to 60 degrees flow straight away! And now it's wired in a way that radiators zone valves open when UFH is ON to make sure that there is some flow through towel rads (we have 3 of them). So I believe it will be ok without additional bypass
 
Thanks a lot! Looks like this solved the issue - added 1 full turn on the internal bypass, set output to Auto and now it goes to 60 degrees flow straight away! And now it's wired in a way that radiators zone valves open when UFH is ON to make sure that there is some flow through towel rads (we have 3 of them). So I believe it will be ok without additional bypass
No problem 😎
 
Thanks a lot! Looks like this solved the issue - added 1 full turn on the internal bypass, set output to Auto and now it goes to 60 degrees flow straight away! And now it's wired in a way that radiators zone valves open when UFH is ON to make sure that there is some flow through towel rads (we have 3 of them). So I believe it will be ok without additional bypass

That's great to hear, you suspected the flow rate originally,
It would be interesting to see if you now can on UFH only or rads only

Did you also increase the pump speed to 100%?,
Also if you get a chance you might post the flow and return temps.

Thanks.
 
That's great to hear, you suspected the flow rate originally,
It would be interesting to see if you now can on UFH only or rads only

Did you also increase the pump speed to 100%?,
Also if you get a chance you might post the flow and return temps.

Thanks.

Can't log in on this PC for some reason or other.
 
If I log off or just exit the forum without logging off and go back in it asks me to log on, it then displays my user name and saved(correct) password but when i select log in nothing happens so I then select "forgot password" it then directs me to my given email and asks me for new password + confirmation, I then enter my (saved )+confirmed) password and press save and I am then logged in, the same happens in the central heating forum but not in the Electrical forum (different user name).
 
Last edited:
That's great to hear, you suspected the flow rate originally,
It would be interesting to see if you now can on UFH only or rads only

Did you also increase the pump speed to 100%?,
Also if you get a chance you might post the flow and return temps.

Thanks.
Pump was always at 100%. Will post some charts on temps later
 
  • Like
Reactions: John.g
Pump was always at 100%. Will post some charts on temps later
It's still a strange one though because if the diverter valve was working originally its hard to understand why not enough water flowed even if the bypass was fully closed, the diverter valve should have directed the primary water to the zone(s) valves which presumably opened at the same time and even one rad/towelrad should provide the minimum flow necessary.
 
Why do I have to reset my password each time I log out since this morning?.
Hi John,

We're toying around with a new advertising partner and that might have something to do with it.

Although it does appear as though your computer isn't remembering your logins, and you're simply resetting your password to login, rather than using the last password you chose?

(Don't ever write passwords in here, I'm sure you wouldn't have done already but I thought I'd let you know and say this)

If it happens again could you please try to clear the browser cookies, close the browser down, then reopen it, login, and check the box to remember you each time you visit (only providing you're using a computer only you have access to.
 
Hi John,

We're toying around with a new advertising partner and that might have something to do with it.

Although it does appear as though your computer isn't remembering your logins, and you're simply resetting your password to login, rather than using the last password you chose?

(Don't ever write passwords in here, I'm sure you wouldn't have done already but I thought I'd let you know and say this)

If it happens again could you please try to clear the browser cookies, close the browser down, then reopen it, login, and check the box to remember you each time you visit (only providing you're using a computer only you have access to.
Thanks Dan, Yes, I'm using my saved password each time in resetting and clicking the remember me box and also the stay logged in box.
 
It's still a strange one though because if the diverter valve was working originally its hard to understand why not enough water flowed even if the bypass was fully closed, the diverter valve should have directed the primary water to the zone(s) valves which presumably opened at the same time and even one rad/towelrad should provide the minimum flow necessary.
Well, I think I spoke too soon. It's doing the same thing again... Adding more turns on the internal bypass did not help - put it back to the original position now. Does this boiler not have a flow rate sensor for the heating circuit? I'm sure the flow rate is good, because I have 3 towel rails all fully open and they heat up very quickly when the boiler outputs 60C.

So the situation now is that it would sit at minimum flame for a while with return temperature about 38 and flow about 42... If I turn the hot water it heats it up perfectly fine - flow goes above 60 immediately... Then after DHW pump overrun it goes back to heating mode and temperature drop to 40 again. What else could be wrong?
 
In heating mode your boiler has a minimum output of 6kw so assuming that this is correct then a deltaT of 4C (flow/return) = a flowrate of > 20 LPM so no problem there it would seem.

Not sure what you mean by DHW pump overrun, if its a combi?? then the primary circ pump (the only one?)
may go in to overrun when finished with DHW and depending on the pump overrun time could reduce the temperature from 60C to 40C but should then fire up on CH/UFH and very quickly go to 60c again. Are you sure that there is nothing (remotely) setting the boiler flow temp to a very low value when CH/UFH requested?.
 
DHW pump overrun is what it shows in the Status menu after I turn the hot water off. After it's done with overrun and back to heating mode - flow temperature doesn't want to go to 60 and stays about 40.
Both zone vales are just simple 240V, no fancy smart controls connected to the boiler itself. So I'm pretty sure there is nothing setting Flow temp to low value
 
Just used your formula to calculate the flow rate assuming it is firing at min 6kW. If I have 4 degrees flow/return difference it gives me 21.5 l/min. Is this reasonable flow for 3 towel rails?
 