Pretty new boiler this guys , went to service it earlier today , service got abandoned because the bleeding thing would not go in to high fire , rang Vaillant, no joy , emailed them , no reply yet , anybody know how to do it , cheers in advance .
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Was you calling for heating and hot water?
Sounds same as a glowworm energy with the mode button...so do you have to get it to P1 then you can set it from 0 to 100...100 being high fire?
Looking at the instructions mate. It looks like you use p1 the bump it up to 100what about PO3
1. Ensure that the gas inlet working pressure can be obtained with all other gas appliances in the property working. 2. Close the gas isolator cock (1). 3. Undo the sealing screw on the measuring nipple (2). 4. Connect a pressure gauge to the measuring nipple (2). 5. Open the gas isolator cock (1). 6. Start up the product with check programme P.01 (system with eBUS controller) or P.03 (system without eBUS controller). 7. In addition, ensure that maximum heat can be dissipated into the heating system by turning up the room thermostat. 8. With the boiler operating at full load check that the gas inlet working pressure at the reference test point (2)Looking at the instructions mate. It looks like you use p1 the bump it up to 100
Just emailed you mate.send it me i will sort it if thats ok