Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

IND_Nick

Esteemed
Gas Engineer
Nov 21, 2012
353
247
43
Morning,

I have a job later this week with the above , Viessmann Vitodens System boiler. It has a 4 pipe setup with internal diverter and at present there is a wireless thermostat/programmer controller in the hallway.
Customer wants a Honeywell Evohome System and I just wondered if I can wire this into the boiler to continue using the 4 pipe system and internal diverter, or do I need to pipe CH flow into a S Plan and just cap the DHW Flow/Return as I can only see 1 L and N available so assume this is for a 240v Heating control.
Any advice appreciated, thanks.
 
i like the 4 pipe I would use weather comp rather than evohome and fit the kit for hot water. But if the customer wants evohome. Rather defeats the object of the 4 pipe system doesn’t it.
 
Just spoke to Viessmann and they do a module that provides a 240v connection for the DHW so can all be wired up and remain with the 4 pipe setup.
The Evohome is because they work from home so want to zone the house, it's a semi that been extended on to extension heating pipes are a mess unfortunately as I'd normally recommend zoning for floors with weather compensation.
 
Working from home and of course they can’t just walk around and shut a few rads down, then open them up later!! 🫣
 
  • Like
Reactions: IND_Nick

Official Sponsors of Plumbers Talk

Similar plumbing topics

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.