Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

N

Nicko131187

hi, im having trouble with a worcester 30si combi boiler, the pressure keeps dropping after 24 hours and having to re pressurise the system in order for it to work again, water is constantly dripping from the pressure relief valve pipe on the outside of the propertie where it exits, i have changed the valve as thought it might be the problem, the pressure when the boiler is on is about 1.5 bar, and doesnt go up when boiler is on so it cant be the expansion vessel. after changing the blow off this problem still occurs.
any help would be great as problem with customer needs solving
Many thanks
 
are you sure the gauge is working ? id isolate the boiler and drain to se if the gauge is stuck unless your very unlucky a new prv shouldnt pass at 1,5bar
 
Yehh tested the gauge, as the old prv was being replaced i drained it by it to see if the gauge was working, and its fine. If the boiler was over pressurising and blowing off i would make sure the expansion was charged or the diaphram in tact but when the boiler runs it doesnt exceed 1.8 bar. You think the new prv may be also faulty? i cant think it could be anything else. Its wierd as all it is is a constant dri0.
Many thanks
 
If the new prv is passing and system pressure is in order then the valve MUST be faulty. Take it back.
 

Official Sponsors of Plumbers Talk

Similar plumbing topics

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.