Problem with this one is when a demand is on, the boiler was firing up for a short time then cutting out and the red light was flashing 4 times per sec. Checked both sensor, and they read within the range stated in MI's. MI's say next to check the resistance across the fan black and white leads, I tested across the fan terminals. MI's say it should be 75ohms to175ohms. I only got 64ohms. Going by MI's it says replace the fan. The fan seems to be running ok tho and the APS is made and ignition starts. APS works ok, although it takes a few seconds for the switch to close after it has been on. The boiler locks out with the cover on and off. When I left tonight it had ran for about 20 mins without lockout, so they're going to phone if it happens again. Would the fan reading low ohms be the problem?? Anything I haven't checked.
Cheers for any help guys, got a little experience in break downs but still learning