Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

FGA Result need altered?

View the thread, titled "FGA Result need altered?" which is posted in UK Plumbers Forums on UK Plumbers Forums.

JTplumbingservices

Gas Engineer
I had to move an existing Vokera unica 32i today for a kitchen upgrade so I stuck my analyser in afterwards, my ratio is fine and reading 0.0011 but the C02 is 9.7 and 213ppm which is high according to the MI.
I’ll be back on the job tomorrow, it’s an empty house and the boiler has been left isolated but should I be adjusting this to get the numbers down?
Cheers in advance.
 
I had to move an existing Vokera unica 32i today for a kitchen upgrade so I stuck my analyser in afterwards, my ratio is fine and reading 0.0011 but the C02 is 9.7 and 213ppm which is high according to the MI.
I’ll be back on the job tomorrow, it’s an empty house and the boiler has been left isolated but should I be adjusting this to get the numbers down?
Cheers in advance.


The gas valve will probably need setting up. You’ll need a 2/2.5mm and 4mm Alankey.

1. Turn the selector control knob to the off position.
2. Drop the PCB down at the back there are 2 screw to undo a flap.
3. Using a pen locate the red button under the flap.
4. Press once for ch max (usually run the hot tap too) press twice for dhw max and press third time for min.
5. Max co should be 9.0 min should be 9.5. (Double check with mis)
6. Once complete turn the boiler on from the selector control knob it’s out of service mode.

Hope that helps.
 
The gas valve will probably need setting up. You’ll need a 2/2.5mm and 4mm Alankey.

1. Turn the selector control knob to the off position.
2. Drop the PCB down at the back there are 2 screw to undo a flap.
3. Using a pen locate the red button under the flap.
4. Press once for ch max (usually run the hot tap too) press twice for dhw max and press third time for min.
5. Max co should be 9.0 min should be 9.5. (Double check with mis)
6. Once complete turn the boiler on from the selector control knob it’s out of service mode.

Hope that helps.
Cheers for that, I get how to alter it. I just wasn’t sure with the ratio being ok and the CO and PPM not ok what the correct course of action was as I’ve never came across it before.
 
defo adjust then wouldnt be surprised if you cant get it down past 140 ppm
 
I wouldn't start altering it until you've checked the burner seals etc. Could be something simple like that. Have you checked your 02 readings on air intake too?
 
Ok mate cheers, I’ve never had to do this before . Is it just a case of adjusting it while it’s running with the analyser in and watch the reading drop as I go ?
I wouldn't start altering it until you've checked the burner seals etc. Could be something simple like that. Have you checked your 02 readings on air intake too?

Wow! JT, I asssume that you are registered? How can you nit have adjusted a gas valve before now, is it not part of training these days. Not trying to be a Smart A, I am genuinely confused - it is a basic function.
Choppers: Before you start worrying about seals, it is normal to reset the gas valve, as they drift. I had to adjust a Worcester yeterday. The CO2 was 9.1% on high. I adjusted but Overstepped, and the CO shot through the roof!. Slight readjust and bang on 9.8, and CO, IIRC, about 95.

If you cannot adjust to correct parameters, then start looking at other stuff.

Or am I missing something?
 
Last edited:
Wow! JT, I asssume that you are registered? How can you nit have adjusted a gas valve before now, is it not part of training these days. Not trying to be a Smart A, I am genuinely confused - it is a basic function.
Choppers: Before you start worrying about seals, it is normal to reset the gas valve, as they drift. I had to adjust a Worcester yeterday. The CO2 was 9.1% on high. I adjusted but Overstepped, and the CO shot through the roof!. Slight readjust and bang on 9.8, and CO, IIRC, about 95.

If you cannot adjust to correct parameters, then start looking at other stuff.

Or am I missing something?
I don’t see why you’re so confused.
No you don’t have to do it as part of training and I haven’t done it yet because I haven’t been installing or moving boilers since I became registered.
Hope this clears things up for you.
 
I don’t see why you’re so confused.
No you don’t have to do it as part of training and I haven’t done it yet because I haven’t been installing or moving boilers since I became registered.
Hope this clears things up for you.

Your tone suggests that you have taken offence!
I can’t actually recall what is in the ACS to get a boiler ticket, but I do know that you use to have to do a FGA course, but is now part of the Boiler module. I still do not understand how you can be registered for boilers, especially as a new guy, without having learnt about FGA’ing - holding the ticket says you are competent.

Has the industry gone mad?
 
Your tone suggests that you have taken offence!
I can’t actually recall what is in the ACS to get a boiler ticket, but I do know that you use to have to do a FGA course, but is now part of the Boiler module. I still do not understand how you can be registered for boilers, especially as a new guy, without having learnt about FGA’ing - holding the ticket says you are competent.

Has the industry gone mad?
Your tone suggested you were actually trying to be a ‘ smart A ‘
We did learn about it and I passed my combustion analysis which I have on my card.
During assessments and training we had to practically carry out FGA tests and record results but never had to physically alter a valve, we learned a lot about ratios and action levels etc but never if a ratio is fine and other readings are not and this is the first time I’ve experienced it.
I thought this site was about helping and advising others ?
To be fair it is 99% of the time.
 
Your tone suggests that you have taken offence!
I can’t actually recall what is in the ACS to get a boiler ticket, but I do know that you use to have to do a FGA course, but is now part of the Boiler module. I still do not understand how you can be registered for boilers, especially as a new guy, without having learnt about FGA’ing - holding the ticket says you are competent.

Has the industry gone mad?

Does it really matter fire least he’s asking as he’s unsure

We can still ask questions we all don’t know everything

If you can help help if not don’t comment simple
 
Your tone suggests that you have taken offence!
I can’t actually recall what is in the ACS to get a boiler ticket, but I do know that you use to have to do a FGA course, but is now part of the Boiler module. I still do not understand how you can be registered for boilers, especially as a new guy, without having learnt about FGA’ing - holding the ticket says you are competent.

Has the industry gone mad?
How about helping rather than busting his chops. For all you know mate. He has been on an estate of 500 boilers where they cannot be adjusted. #justsaying
 
Your tone suggested you were actually trying to be a ‘ smart A ‘
We did learn about it and I passed my combustion analysis which I have on my card.
During assessments and training we had to practically carry out FGA tests and record results but never had to physically alter a valve, we learned a lot about ratios and action levels etc but never if a ratio is fine and other readings are not and this is the first time I’ve experienced it.
I thought this site was about helping and advising others ?
To be fair it is 99% of the time.
Don’t worry about it mate. Nobody knows everything, no matter how smart they think they are.
 
Well, have it your way. I was not trying to be unpleasant, but it is shocking that you are classed as competent while never having adjusted a gas valve. That is not your fault, but the state of the training in this industry. TBF, though, I would have thought your first course would have been to download the MIs and get studying. Don’t rely o advice here, it is often wrong
 
Well, have it your way. I was not trying to be unpleasant, but it is shocking that you are classed as competent while never having adjusted a gas valve. That is not your fault, but the state of the training in this industry. TBF, though, I would have thought your first course would have been to download the MIs and get studying. Don’t rely o advice here, it is often wrong
I’ll be sure to contact you directly from now on whenever I need advice seen as how you knew everything there is to know from day 1, and believe me there are lots out there with gas tickets who are completely incompetent and dangerous who would just go ahead and start messing about with things they don’t know about without seeking advice. Yes I may not have been sure about this as I’ve never done it but that’s why I’m seeking advice from people on here with experience.
 
I’ll be sure to contact you directly from now on whenever I need advice seen as how you knew everything there is to know from day 1, and believe me there are lots out there with gas tickets who are completely incompetent and dangerous who would just go ahead and start messing about with things they don’t know about without seeking advice. Yes I may not have been sure about this as I’ve never done it but that’s why I’m seeking advice from people on here with experience.
You did the right thing mate. If I’m doubt. ASK.
 
I haven't read all the posts above but lets keep this forum like it is intended , to help members . Please do not turn it into facebook .

However I am absolutely astounded that somebody would actually move a Vokera , wants to go in a skip if you ask me.
 
Next time you get readings like that just check the 02 % coming in at the test point, providing it has one, if it doesn't have one put your tester probe on the inlet in the boiler at the bottom of the flue turret. If you get any Co ppm readings you'll now the flue seals will need looking at. Another sign the flue seals have failed or are damaged is if the Co readings fluctuate up and down when you test it.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "FGA Result need altered?" which is posted in UK Plumbers Forums on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Sponsors

Thread statistics

Created
JTplumbingservices,
Last reply from
billski,
Replies
31
Views
951
Back
Top