I have a Worcester heatslave 15/19 oil fired boiler. The expansion tank was recently replaced however I am still having issues where the hot water pressure is not consistent.

Examples being you run the kitchen tap and it seems to take a while for the hot water to come out but then when it does come out it runs hot and is fine.
In addition we have an oldish triton shower which has a thermostatic mixer the water from the shower will run hot for a while then runs cold and goes in this repeated pattern. I am confident that there is no issue with any fault on the shower, when the shower is running you can feel the hot water pipe elbow joint next to the shower unit and can feel the pipe going from hot to cold in sync with the hot and cold water coming out the shower head when it should just be consistently hot.

All the radiators were bled after the expansion vessel was fitted and the bled valves on the boiler have also been bled. The motor is fine therefore after doing lots of research on the net so far I am still trying to find out what could be causing this.

Any suggestions would be appreciated. Thanks
 
So is the issue pressure or flow or temperature?

Simong - thanks for responding. From what you have said the flow of the water doesn’t change the temperature just drops. When you feel the shower pipe you can feel the temperature very quickly dropping from hot to cold and then the reverse about 5-10 seconds later. Thanks
 
I have a Worcester heatslave 15/19 oil fired boiler. The expansion tank was recently replaced however I am still having issues where the hot water pressure is not consistent.

Examples being you run the kitchen tap and it seems to take a while for the hot water to come out but then when it does come out it runs hot and is fine.
In addition we have an oldish triton shower which has a thermostatic mixer the water from the shower will run hot for a while then runs cold and goes in this repeated pattern. I am confident that there is no issue with any fault on the shower, when the shower is running you can feel the hot water pipe elbow joint next to the shower unit and can feel the pipe going from hot to cold in sync with the hot and cold water coming out the shower head when it should just be consistently hot.

All the radiators were bled after the expansion vessel was fitted and the bled valves on the boiler have also been bled. The motor is fine therefore after doing lots of research on the net so far I am still trying to find out what could be causing this.

Any suggestions would be appreciated. Thanks
 
It is a combi. If it was scale you would have reduced flow. If it was divertor than hot water isn't affected but you would get warm rads with heating off.
 
Simong ok thanks will look into it further

In relation to this old post we ended up gutting the bathroom as it needed doing and replacing everything. We have put a new triton shower in and had a plumber move the pipe work from under the floor to where it is accessible. Upon using the shower we are still getting intermittent hot and cold water. This doesn’t happen on any of the taps. This leads me to believe the problem has to be with the boiler.
 
Are any of the other taps mixer taps, specifically ones where the hot/cold freely mix within the body as opposed to one’s where a divided flow is maintained until the end of the spout?
 
If all hot taps are fine and only shower doesn’t work it doesn’t seem likely that the boiler is faulty.

Either faulty/ non-existent non return valves for shower?

Or flow through shower is not enough to keep boiler firing. This could be a number of reasons......

Blocked inlet filter to shower hot

Restrictors in shower supplies ( these often have to be removed for a Combi

“Eco flo” setting on shower , remove stop in flow handle.

Restrictive hose/head .....,

Or possibly new shower is faulty.

Get plumber to look at all of above ; if it’s a bar mixer it is trivial to swap it out for another known to be working one to eliminate boiler.
 
If all hot taps are fine and only shower doesn’t work it doesn’t seem likely that the boiler is faulty.

Either faulty/ non-existent non return valves for shower?

Or flow through shower is not enough to keep boiler firing. This could be a number of reasons....

Blocked inlet filter to shower hot

Restrictors in shower supplies ( these often have to be removed for a Combi

“Eco flo” setting on shower , remove stop in flow handle.

Restrictive hose/head ...,

Or possibly new shower is faulty.

Get plumber to look at all of above ; if it’s a bar mixer it is trivial to swap it out for another known to be working one to eliminate boiler.



Hi, many thanks for the above reply appreciate everyone’s time and answers. I think will arrange for a plumber to look at it. Thanks
 
Hi,
I would agree with Ben-gee. Very unlikely to be a boiler fault.
The length/size of the pipes could have an effect on both flow and temp.
Personally, I would have advised a good electric shower. Thus ensuring hot water for washing in the event of a boiler fault (combi).
 
It sounds like the boiler is not able to keep up with the demand being placed on it by the hot water draw off for some reason, assuming you are meaing it goes from hot to cold and remains cold until water turned off, rather than cycling between hot and cold whilst running. If it were the heat exchanger then apart from the initial few seconds burst of hot water, it would never deliver hot water to the shower.

I suspect the shower remains hot if not turned on to full capacity. If so, a quick fix might be to change the shower head to an eco water saving version.
 
It sounds like the boiler is not able to keep up with the demand being placed on it by the hot water draw off for some reason, assuming you are meaing it goes from hot to cold and remains cold until water turned off, rather than cycling between hot and cold whilst running. If it were the heat exchanger then apart from the initial few seconds burst of hot water, it would never deliver hot water to the shower.

I suspect the shower remains hot if not turned on to full capacity. If so, a quick fix might be to change the shower head to an eco water saving version.

Hi, it alternates between hot and cold so it might warm up then stay hot for 30seconds to a 1 minute then it will gradually go cold for the same amount of time then go gradually hot again it’s like a rotation. We tested it again yesterday and it seems that it will stay consistently hot if you don’t touch the temperature gauge on the shower. But if the next person gets in who wants the temperature slightly lower and they turn the knob this then makes the shower then run hot and cold throughout the use of the shower for that period of time....
 
Hi, it alternates between hot and cold so it might warm up then stay hot for 30seconds to a 1 minute then it will gradually go cold for the same amount of time then go gradually hot again it’s like a rotation. We tested it again yesterday and it seems that it will stay consistently hot if you don’t touch the temperature gauge on the shower. But if the next person gets in who wants the temperature slightly lower and they turn the knob this then makes the shower then run hot and cold throughout the use of the shower for that period of time..

Can you measure the flow rate from the shower when its "consistently hot" and then again when when running hot&cold, if the 15/19 boiler gives say ~ 17kw on hot water then you should get ~ 10 LPM at 40C .
 
Does it stay the correct temperature if you run a hot tap slightly elsewhere to increase the demand? If so, I'd be looking at a flow switch fault

Hi, I finally managed to get a boiler engineer\plumber to come out today and he has had a quick look and believes it is an issue with the flow switch. When the hot tap is run in the bathroom at the same time as the shower then the shower does appear to stay the correct temperature. I have ordered a new flow switch. I have read some things on some plumbing forums where some people have been able to fit the new flow switch themselves. To replace the flow switch is it a case of turning the boiler off then isolating the mains inlet valve and removing the existing flow switch and attached sensor then putting the new one in situ then reopening the flow for the mains inlet? Thanks
 
I have read some things on some plumbing forums where some people have been able to fit the new flow switch themselves. To replace the flow switch is it a case of turning the boiler off then isolating the mains inlet valve and removing the existing flow switch and attached sensor then putting the new one in situ then reopening the flow for the mains inlet? Thanks

No. It's a job that needs to be done by a plumber or heating engineer who is on the Gas Safe Register. A legitimate GSR may well refuse to fit a flow sensor that you have bought yourself because they need to be sure it is the correct and genuine spare part.
 
No. It's a job that needs to be done by a plumber or heating engineer who is on the Gas Safe Register. A legitimate GSR may well refuse to fit a flow sensor that you have bought yourself because they need to be sure it is the correct and genuine spare part.

Thanks for the reply. The boiler is an oil fired boiler so I don’t think being gas safe registered applies. I have replaced other parts on the boiler last year without issue. Any other replies would be appreciated from anyone who has knowledge of this particular type of boiler. In case the thread doesn’t say it’s a Worcester Heatslave 15/19 RSO.
 
Hi, I finally managed to get a boiler engineer\plumber to come out today and he has had a quick look and believes it is an issue with the flow switch. When the hot tap is run in the bathroom at the same time as the shower then the shower does appear to stay the correct temperature. I have ordered a new flow switch. I have read some things on some plumbing forums where some people have been able to fit the new flow switch themselves. To replace the flow switch is it a case of turning the boiler off then isolating the mains inlet valve and removing the existing flow switch and attached sensor then putting the new one in situ then reopening the flow for the mains inlet? Thanks
I believe your boiler is a storage combi and has a heatslave tank that holds 45 litres of hot water, when there is a demand for hot water, the flow switch starts up the circ pump to circulate the hot water from this storage tank through a heat exchanger which heats the water passing through it. A thermostat in the storage tank controls the temperature by firing the boiler on/off.
I know the flow switch is the suspected fault but if you open a hot tap only and if the water temperature is and stays normally hot then that would tend to rule out the switch, when the water starts flowing first then if the stored water is at its correct set point then one would think that the boiler should not start up until the tank temperature falls to its cut in point. It might be worth checking out the tank thermostat as well when changing that flow switch.
 
I believe your boiler is a storage combi and has a heatslave tank that holds 45 litres of hot water, when there is a demand for hot water, the flow switch starts up the circ pump to circulate the hot water from this storage tank through a heat exchanger which heats the water passing through it. A thermostat in the storage tank controls the temperature by firing the boiler on/off.
I know the flow switch is the suspected fault but if you open a hot tap only and if the water temperature is and stays normally hot then that would tend to rule out the switch, when the water starts flowing first then if the stored water is at its correct set point then one would think that the boiler should not start up until the tank temperature falls to its cut in point. It might be worth checking out the tank thermostat as well when changing that flow switch.
Hi, thanks for your reply as I mentioned I had a plumber/boiler engineer come around yesterday he has already diagnosed the fault as the flow switch. Due to the time it has taken to get a plumber I’m trying to ascertain if the flow switch is something I can replace myself and if it’s just a case of isolating the cold water inlet supply either on the boiler or at the mains in order to remove the old part and install the new one. Thanks
[automerge]1568367024[/automerge]
My bad - I missed that. You are correct Gas Safe is not applicable and the regulations are not as strict. I would still, however, recommend that you employ a OFTEC registered technician to do the work.

If anyone else can answer my original point that would be appreciated.
 
Last edited:
Test the flow switch first with a multi meter, if your plumber has done this, why not get him to replace it?
Easy repair, less than an hours labour.
However, I would (as John.g suggested) test slave tank stat. first.
All straight forward stuff really.
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Hot water pressure issue" which is posted in Bathroom Advice on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread statistics

Created
ajt2018,
Last reply from
Tea-Break,
Replies
34
Views
5,324
Back
Top