Thought I'd share this with you as it happened to me yesterday! Maybe others can share their experience of attending reported CO poisoning.
Landlord rang me yesterday regarding an incident involving the fire-brigade. He said they've turned the gas off at a property I look after!! Sphincter starts putting!! However I recollect the property and knew that it has a combi and hob! Combi is negative pressure so not a likely suspect!
Transco had been and done there thing by the time I got there! So the tenants (asylum seekers) has experienced the fire-brigade with huge fans evacuating the premise and transco slapping a big notice saying DO NOT USE!!!
Soundness test - pass, Visual of the appliances, pass flue's a bit close to a window but the window isn't openable! FGA results of the boiler 115ppm/0.0010 on High 56ppm/0.0008 Low. Nothing outside the unit or the flue through the wall.
Now here's where my brain thinks "how you suppose to test a hob?" Anyways set all 4 away and visually okay so hovered the fga above the burners looking for dodgy amounts of CO. Got 5ppm max!
I then spent an age re-assuring the tenants that everything was okay. I then had to go through the same explanation with the landlord. He also insisted on something in writing !!! I haven't got a clue what caused the tenants 'headaches' but it certainly weren't fumes!!
My pondering is though, did i do enough? Could I have checked anything differently? It's not every day you attend reported CO poisoning involving the fire-brigade 🙂 Sheeeeeeeeeeesh!!!
Thought I'd share this with you as it happened to me yesterday! Maybe others can share their experience of attending reported CO poisoning.
Landlord rang me yesterday regarding an incident involving the fire-brigade. He said they've turned the gas off at a property I look after!! Sphincter starts putting!! However I recollect the property and knew that it has a combi and hob! Combi is negative pressure so not a likely suspect!
Transco had been and done there thing by the time I got there! So the tenants (asylum seekers) has experienced the fire-brigade with huge fans evacuating the premise and transco slapping a big notice saying DO NOT USE!!!
Soundness test - pass, Visual of the appliances, pass flue's a bit close to a window but the window isn't openable! FGA results of the boiler 115ppm/0.0010 on High 56ppm/0.0008 Low. Nothing outside the unit or the flue through the wall.
Now here's where my brain thinks "how you suppose to test a hob?" Anyways set all 4 away and visually okay so hovered the fga above the burners looking for dodgy amounts of CO. Got 5ppm max!
I then spent an age re-assuring the tenants that everything was okay. I then had to go through the same explanation with the landlord. He also insisted on something in writing !!! I haven't got a clue what caused the tenants 'headaches' but it certainly weren't fumes!!
My pondering is though, did i do enough? Could I have checked anything differently? It's not every day you attend reported CO poisoning involving the fire-brigade 🙂 Sheeeeeeeeeeesh!!!