does this sound ok, cant find my old post but I have been redoing my portfolio and here it is

for boiler installs and services:
Visual checks = fine
Let by test = fine
Tightness test = fine
Working pressure = 0.8mb drop = fine, Gas rate-within MI spec.
spillagetest – fine, flue check – fine (no signs of distress),
Flue within minimum distances fromopening/ obstruction – fine

Bonding on meter, all fittings ok andpipe sealed in the wall, flame picture – fine, appliance seal- fine

Initial tightnesstest

Let by test pressure........10mb...... Pressure rise......0.................. Pass/Fail........Pass.......................

Stabilisation pressure....20mb........... Stabilisation time...1 mins..............

Allowable Pressure drop for pipe work............0mb......................in2 mins


Static pressure at meter...........23mb.....................

Allowable Pressure drop with appliances connected....4mb..............

Test pressure...20mb............ Test time......2 mins............ Pass/Fail
Give reasons for pass or fail.
All working fine, no leaks


then for the techincal details:

Working pressure at meter.......20mb...................

Working pressure at appliance.....19.2mb..............

Burner pressure…………………………15mb………


Flue gasanalyser readings

CO2................2.4.........................

CO...................25.........................

CO/CO2Ratio..........0.0010.........


Gas ratecalculation
Meter start...892.974...........................................
Meter Finish....893.061........................................
Actual Gas rate per hr....2.62m3..........................
M/I gas rate per hr.....2.6m3 p/h..........................






 
That's only one open flue isn't it? This is room sealed ?? To be honest I'm not sure what that is?? Will look into that??
Also have pipe sizing chart on the installs,
 
There's a lot of duplication in there and it looks very untidy to me.

I would be looking for something along the lines of :-

BOILER INSTALLATION AND SERVICE RECORD.


Make and model of boiler

Visual condition of boiler Pass/Fail

Notes.

Visual Condition of pipework Pass/Fail

Notes.

Condition of meter Pass/fail

Notes.

Main equipotential bonding Pass/Fail

Notes.

Let By Test Test Pressure mb Pass/Fail

Notes.

etc. and in the notes state why the appliance has passed or failed that particular test and possibly the method of testing where necessary.

You need to make it easy for the assessor to pass your portfolio and see that you understand what you have been doing.
 
I said no flue flow, BECAUSE you had done spillage, they go together, yes on open flued only, but you started it haha
 
Get a copy of a Landlords Safety Check and an installation checklist (benchmark etc) this will give you an idea of what you should be doing
 