Install the app
How to install the app on iOS

Follow along with the video below to see how to install our site as a web app on your home screen.

Note: This feature may not be available in some browsers.

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Hobo128

Gas Engineer
Nov 15, 2009
292
32
28
Manchester
Gas rating a greenstar 30si. Put in service mode-2min test meter index 0.095. 0.095x3600x10.76/120 =30.666kw
In the technical data this matches what it says for maximum rated heat output dhw.
If you covert 30.666kw to m3/h 30.666x0.095 = 2.91327m3/h. In the technical data it says it should be 3.24m3/hr
Tb141 says it can be 10% below MI so 3.24 x 0.1 = 0.324 (10% of 3.24) 3.24-0.324 = 2.916
So the absolute minimum it can be is 2.916m3/h and im getting 2.91327m3/hr. Am I ok ?????
 
I make 30.66 kw 3.14 m3/h Even by your figures tho its so little I wouldn't worry about it, if you are adjust the air gas ratio valve a bit as its prob not bang on.
 
???? why times it by 3600 and divide by 120?

we just learnt x 30= m3/hr x 10.77 = kw.
 