Hi
I’m currently working on a 3 story house that’s being converted into 4 flats. I installing 40kw boiler, 15 rads, 4 Heating zones plus a hot water zone. Etc etc
Each flat has a kitchen sink, toilet, basin and electric shower.
Problem is, I’ve got a 15mm rising main. ‭Im hoping it’ll just be adequate.
However as back up I’ve thought about installing a booster set.
As a back up to the back up I’ve thought about installing a break cistern then a booster set.
I wondered if you had some experience and thoughts on this?
I’m sort of dreading telling the client that he needs a 25mm rising main, especially when the main also supplies 2-3 buildings. Thanks...Dan
 
Hi
I’m currently working on a 3 story house that’s being converted into 4 flats. I installing 40kw boiler, 15 rads, 4 Heating zones plus a hot water zone. Etc etc
Each flat has a kitchen sink, toilet, basin and electric shower.
Problem is, I’ve got a 15mm rising main. ‭Im hoping it’ll just be adequate.
However as back up I’ve thought about installing a booster set.
As a back up to the back up I’ve thought about installing a break cistern then a booster set.
I wondered if you had some experience and thoughts on this?
I’m sort of dreading telling the client that he needs a 25mm rising main, especially when the main also supplies 2-3 buildings. Thanks...Dan

I think you've hit the nail on the head with the tank and pump set.

How high is the Building and what is the Static pressure at ground level?
 
I think you've hit the nail on the head with the tank and pump set.

How high is the Building and what is the Static pressure at ground level?

Thanks s lot 🙂 well I’ve got 2.5 bar at ground, then top outlet is about 7 M up. So I recon 0.7 Bar loss. Minus equivalent pipe length, minus fittings.

Thing is there’s really no chance of having mains pipe re-run in 25mm. So you recon a break cistern and booster set is way to go then?
 
Thanks s lot 🙂 well I’ve got 2.5 bar at ground, then top outlet is about 7 M up. So I recon 0.7 Bar loss. Minus equivalent pipe length, minus fittings.

Thing is there’s really no chance of having mains pipe re-run in 25mm. So you recon a break cistern and booster set is way to go then?

Can you get 22mm pipe upto the flat ?
 
Thanks s lot 🙂 well I’ve got 2.5 bar at ground, then top outlet is about 7 M up. So I recon 0.7 Bar loss. Minus equivalent pipe length, minus fittings.

Thing is there’s really no chance of having mains pipe re-run in 25mm. So you recon a break cistern and booster set is way to go then?
I do think you are best with that set up but you will need to increase the size of the riser anyway in my opinion.
Personally, I would use 22 mm Copper, it needs calculating though.
The 15mm would be too restricted and noisy. (if that is what you are thinking)
 
I do think you are best with that set up but you will need to increase the size of the riser anyway in my opinion.
Personally, I would use 22 mm Copper, it needs calculating though.
The 15mm would be too restricted and noisy. (if that is what you are thinking)

Thanks for advise. Yeah I was thinking of running all cold pipe work from outlet of booster set pump in 22mm. Then reducing down to 15mm say 2M before appliances.

Does that sound right to you? Thanks 🙂
 
Thanks for advise. Yeah I was thinking of running all cold pipe work from outlet of booster set pump in 22mm. Then reducing down to 15mm say 2M before appliances.

Does that sound right to you? Thanks 🙂

Thought you said you couldn't get 22mm upto the flat ?
 
15mm will definately not do three apartments bud you can only get out what you put in 15mm wont even do the unvented cylinder you need a re think . kop
 
  • Like
Reactions: Scott_D
yea you will be ok if you only have 15mm into the break tank just need to size it so it can cope with peak demand and then 28mm into the pump from the tank and then 22mm to the flat

will the pump supply the whole building?
 
  • Like
Reactions: dan_the_plumber