A glowworm 50BF is a fairly basic boiler. It does not have a permanent live. As long as the mechanical pilot light is lit, when a live is applied to the boiler, it will fire and run until it reaches operating temperature. Thereafter it will shut off, turning on once the temperature falls below the set point level.
If the boiler is “randomly” firing that can only be because the boiler is receiving a live (+240v) feed and is below the set temperature.
If the boiler has been wired with a permanent 240v supply it will operate 24/7 switching off when it reaches set temperature and on again as the temperature falls below the set point.
In that configuration any external controls may operate the pump and open / close valves, but will not call the boiler for heat - the boiler is operating independently feeding the heating system when the pump runs.
You should not be replacing parts on a whim.
Any credible heating engineer should be able to diagnose and resolve the issue. A heating engineer that has not checked out the control wiring is not credible.
It is also important to know what the system is. Is it gravity hot water and pumped heating or pumped hot water and heating. If it is the latter has it recently been converted from gravity hot water? - That can cause a host of issues if not done properly.
At the end of the day, the boiler will only fire when it is in receipt of a live feed -so your Engineer needs to find out where it is coming from.
If the boiler is “randomly” firing that can only be because the boiler is receiving a live (+240v) feed and is below the set temperature.
If the boiler has been wired with a permanent 240v supply it will operate 24/7 switching off when it reaches set temperature and on again as the temperature falls below the set point.
In that configuration any external controls may operate the pump and open / close valves, but will not call the boiler for heat - the boiler is operating independently feeding the heating system when the pump runs.
You should not be replacing parts on a whim.
Any credible heating engineer should be able to diagnose and resolve the issue. A heating engineer that has not checked out the control wiring is not credible.
It is also important to know what the system is. Is it gravity hot water and pumped heating or pumped hot water and heating. If it is the latter has it recently been converted from gravity hot water? - That can cause a host of issues if not done properly.
At the end of the day, the boiler will only fire when it is in receipt of a live feed -so your Engineer needs to find out where it is coming from.