Are you running the UFH at very high flow/return temps? if not, what are the (mixed) flow/return temps and
what is the flowrate through each loop?
My basic calculations assume that you are using 100M, 16mm loops which will have a ID of 12mm, a 12mm ID pipe will contain 0.113L/M so total of (9+8)x100x0.113=192L in UFH pipework, say another 85L for the boiler+12 rads = total system contents of 277L. Assume max mean temperature of 60C if whole system in service. At 60C, expansion is 1.62%, a 12L E.Vessel with a precharge pressure & a filling pressure of 1bar will result in a final pressure of 2.2bar, if mean system temperature is 55C, expansion 1.36%, then final pressure is 1.92bar. You should be OK IMO, you can see the boiler pressure with a hot system anyway.
(From water at 15C) | |
Water | |
Temp | Exp |
Deg.C | % |
50 | 1.124 |
55 | 1.36 |
60 | 1.62 |
65 | 1.83 |
70 | 2.18 |
75 | 2.48 |
80 | 2.8 |
85 | 3.13 |
90 | 3.49 |
95 | 3.85 |
100 | 4.24 |
100 | 4.64 |
105
| 5.05 |
Strange all right re boiler stat.