Yes but remember you don't have any control
Over the heat output of the UFH since you have no control of the mixing temperature, this will have to be sorted out.
 
Yes but remember you don't have any control
Over the heat output of the UFH since you have no control of the mixing temperature, this will have to be sorted out.
The pump set is only 3 weeks old are you suggesting the mixing valve could be faulty? Hence the water entering the manifold at a temperature higher than the set value?
 
Possibly but unlikely, the boiler circ pump pressure though at 1.4bar or whatever may be preventing it from operating correctly which is why I suggested throttling it somewhere. Most boiler circ pumps will only be running with a head of 4M (0.4bar) or so. I throttling it works, re install your old pump.
 
Possibly but unlikely, the boiler circ pump pressure though at 1.4bar or whatever may be preventing it from operating correctly which is why I suggested throttling it somewhere. Most boiler circ pumps will only be running with a head of 4M (0.4bar) or so. I throttling it works, re install your old pump.
Yes I agree re installing old pump, I will try throttling the pump back again and also turn the manifold pump back to 2, it’s currently set on 3. I must admit the floors are heating up better with the new pump set as opposed to the pump set on the good manifold. John thank you very much for all the information you have supplied to me. To balance a ufh manifold is it only done with the flow meters, or can you slow the return water?
 
Possibly but unlikely, the boiler circ pump pressure though at 1.4bar or whatever may be preventing it from operating correctly which is why I suggested throttling it somewhere. Most boiler circ pumps will only be running with a head of 4M (0.4bar) or so. I throttling it works, re install your old pump.
I wouldn't reduce the flow rate excessively as the loops are parallel circuits and you want to keep the flows equal, temperature control is the way go INO.




temperature reduction/control is the way to go O
 
I wouldn't reduce the flow rate excessively as the loops are parallel circuits and you want to keep the flows equal, temperature control is the way go INO.




temperature reduction/control is the way to go O
Hi John, well I have throttled back the boiler pump to 1 bar and the manifold pump to speed setting 2 and I achieved 65 degrees flow, and 49 degrees return at the boiler and 45 degree flow through the manifold and 35 return. The boiler is cycling though of 15 mins on 1.15 mins off. I feel we are getting somewhere 🙂
 
  • Like
Reactions: John.g
Numbers not adding up there as the boiler return temp should be the same as the manifold return temp at 35C (assuming UFH only on)



1657032541904.png
 
Numbers not adding up there as the boiler return temp should be the same as the manifold return temp at 35C (assuming UFH only on)



View attachment 76398
Hi John I thought that as well, yes underfloor only on, once the manifold was up to temp would the excess water return back to boiler, making the boiler return higher? I did notice however that with the boiler thermostat set to 60, the flow did get as high as 70 at one point. I see there are two ports on either side on the top of the boiler ther thermostat probes are in the left, I am picking that has actually been set up correctly.
 
Maybe this TMV is sending mixed flow temperature water back to the boiler?, I always thought it was supposed to be the UFH cold water return.
The boiler thermostat should control the flow temperature at whatever setpoint its set to.
Did you check that the boiler flow and return pipes are installed correctly?.
 

Attachments

  • UFH Troubled Rev1.jpg
    UFH Troubled Rev1.jpg
    905.4 KB · Views: 38
Maybe this TMV is sending mixed flow temperature water back to the boiler?, I always thought it was supposed to be the UFH cold water return.
The boiler thermostat should control the flow temperature at whatever setpoint its set to.
Did you check that the boiler flow and return pipes are installed correctly?.
interesting you say that because yesterday the laundry manifold had a flow of 60 at the boiler and returning 59, and that water has to travel 55m there and back.
I checked the flow and return out of the boiler, and the seem to be ok.
Another thought I’ve just had, I think this boiler is way undersized even at the original 35kw. This diesel boiler replaced a 26kw gas boiler which ran all the rads and trench heating and replaced a 16 kw heat pump that was to small to run the underfloor heating, hence why we decided to change. Is there a formula to work out what size boiler one would need.

We already know that when the troubled manifold is on it needs 24.7kw.
 
interesting you say that because yesterday the laundry manifold had a flow of 60 at the boiler and returning 59, and that water has to travel 55m there and back.
I checked the flow and return out of the boiler, and the seem to be ok.
Another thought I’ve just had, I think this boiler is way undersized even at the original 35kw. This diesel boiler replaced a 26kw gas boiler which ran all the rads and trench heating and replaced a 16 kw heat pump that was to small to run the underfloor heating, hence why we decided to change. Is there a formula to work out what size boiler one would need.

We already know that when the troubled manifold is on it needs 24.7kw.

What’s the flow rate of all the zones on this manifold ?
 
What’s the flow rate of all the zones on this manifold ?
Out of the 7 zones, only 4 are operating as the other zones are turned off. 2 x 2.4LPM, 1 x 2.0LPM and 1x 1.5LPM (small laundry circuit) so approx 8.3 lpm in total. This manifold is 55 m away from the boiler.
 
interesting you say that because yesterday the laundry manifold had a flow of 60 at the boiler and returning 59, and that water has to travel 55m there and back.
I checked the flow and return out of the boiler, and the seem to be ok.
Another thought I’ve just had, I think this boiler is way undersized even at the original 35kw. This diesel boiler replaced a 26kw gas boiler which ran all the rads and trench heating and replaced a 16 kw heat pump that was to small to run the underfloor heating, hence why we decided to change. Is there a formula to work out what size boiler one would need.

We already know that when the troubled manifold is on it needs 24.7kw.
Something definitely very strange, I get a UFH heat output of 5.8kw at your flowrate of 8.3LPM and dT of 10C which should only result in a boiler flowrate of 2.77LPM at a boiler return temp of 35C., the measured return is 49C which means that 2.42LPM at 65C is either bypassing through the TMV or through a external bypass to give a boiler return flow of 5.2LPM. But the boiler is outputting ~ 24kw based on your burner cycling times, you may be losing up to 5kw in all that pipework if uninsulated but still wouldn't remotely account for that boiler output, the only logical explanation is that there is another zone (maybe rads) on as well, taking the few temperatures I suggested will show if the TMV is by passing but will not explain the very high boiler output.
 
Which is 4kw required so very strange why it needs 5 x that
Something definitely very strange, I get a UFH heat output of 5.8kw at your flowrate of 8.3LPM and dT of 10C which should only result in a boiler flowrate of 2.77LPM at a boiler return temp of 35C., the measured return is 49C which means that 2.42LPM at 65C is either bypassing through the TMV or through a external bypass to give a boiler return flow of 5.2LPM. But the boiler is outputting ~ 24kw based on your burner cycling times, you may be losing up to 5kw in all that pipework if uninsulated but still wouldn't remotely account for that boiler output, the only logical explanation is that there is another zone (maybe rads) on as well, taking the few temperatures I suggested will show if the TMV is by passing but will not explain the very high boiler output.
I’m with you John it is very strange. All pipe work is insulated, we have doubled checked the flow and return today and all seems ok. There is an external bypass on the boiler but nothing seems to be flowing through it, as the pipes are cold. I wonder if it because of the stupid pump setup on the laundry manifold it’s bypassing and going back to the boiler. I’m about ready to rip the whole system out 😂😂😂 I really can’t find an answer.
 
Bypass on its own shouldn't increase boiler demand,
Can you just run on DHW demand only and see what kind of cycling and flow/return temps you are getting.
Also ensure you check those manifold temperatures sometime.
 
Bypass on its own shouldn't increase boiler demand,
Can you just run on DHW demand only and see what kind of cycling and flow/return temps you are getting.
Also ensure you check those manifold temperatures sometime.
Ok, I’ll go do that now. I have turned the manifold temperatures down like you suggested yesterday. (Is that what you mean)
 
No, the next time the troubled manifold is on check the temperatures where highlighted with the heat gun as suggested in post 69, we can then see if that TMV is bypassing.
 

Attachments

  • UFH Troubled Rev1.jpg
    UFH Troubled Rev1.jpg
    905.4 KB · Views: 37
No, the next time the troubled manifold is on check the temperatures where highlighted with the heat gun as suggested in post 69, we can then see if that TMV is bypassing.
Ok, yes i wil do that. Well I ran the DHW system and this was the result

View attachment 76410
But also while I was standing there, I think I've discovered the problem. We have two pipes running from the boiler to the gas boiler as the radiators are piped to work on gas if something happens to the boiler. On further inspections these flow and return pipes are exceptionally hot, and the DHW is in the complete opposite direction. As you can see from the photos there are 2 valves but these are only shut if the rads are operating by the gas boiler. So it would seem we have flow going along these pipes circulating into the gas boiler, and heading back to the other boiler. This is a 28m loop
( I do hope that makes sense ) This would also explain why the boiler return temperature is higher than the manifold return temp.
Screen Shot 2022-07-06 at 10.10.45 PM.png
tempImageE3NnDP.png
tempImagehjjBPR.png
tempImage4yasaS.png
 

Attachments

  • tempImage09OGie.png
    tempImage09OGie.png
    3.1 MB · Views: 44
Can you shut those valves temporarily and put a note on the gas boiler to that effect and see how the UFH operates.