This sounds as if you need a second independent opinion from another gas safe registered plumber. Just go on the gas safe website for contact details. It will put your mind at rest if nothing else.
Any doubts about running the pipe up the front of the house from the meter into the eaves through into my loft space and then down into my boiler. Also as another point have any of you come across any good external trunking to cover the pipe that can be painted etc... Also i have read that the pipe if painted needs to be yellow?
A run that long is likely to need some 28mm pipe on it.
TB, it doesn't matter if appliances were connected there was a smell of gas so NO drop allowed
The smell of gas has been resolved (due to another leak) but there's still a small drop as I understand it?
Or is it once there's been the smell of gas reported it has to be 100% tight? It's not something I've ever thought about as I've never left a leak unattended to
Once a smell of gas has been reported the installation has to be 100% even if the source of the smell appears to have been resolved.
Reactions: 2 people
Yes the original leak was found and solved but it would appear that we would have a leak elsewhere due to the pressure drop, however we could not identify where
If the guy has isolated the appliances and there is still a drop then probably the best plan would be a new gas run! It could take ages to find a leak on the pipework, specially if its hidden pipework!
Hi, I may not be reading the op right but did he do full test i.e. the let by & tightness test? Was it pipe work only or did it include the boiler aswell? I have not heard about building regs not allowing running copper pipe externally for gas, so will have too look that up.
You need to be careful here, personally i would get someone else to do a tightness test before going to the expense of rerouting the gas in a larger size.
Your in quite an awkward position on the one hand you dont want to be seen as second guessing your gas fitter, but then you dont want to be taken for a mug either.
There's no problem with running copper externally, the issue is protecting it from damage.
It's covered in B.S. 6891:2005+A2:2008 8.15.2 Above ground external pipework.
Above ground external pipework shall be protected against the risk of mechanical damage, e.g. in car ports
So any pipework run along a driveway should be protected from mechanical damage. This could be achieved using a mechanical means to protect copper but it's easier and cheaper to run low carbon steel which is inherently more resistant to damage.
And theft
If there has been a reported gas leak no drop can be left, smell or not.
thats not actually true ive been called to reported leaks where another gsr/ hob fitter had tested and found a 2 mb leak and have just confirmed its only 2 mb and the customer hasnt smelt anything so just confirmed with them its ok to leave generally you dont get called to a leak unless the owner has smelt it
but i do agree in this case it should have been capped and labeled
can the new run not be run high level to remove the mechanical/theft problem
It is Steve
DEALING WITH SUSPECTED GAS ESCAPES
When responding to the following situations, the gas installation shall be tightness
tested in accordance with clause 5.3.2 (existing installations). However, to
successfully pass the test, there shall be no perceptible movement of the gauge
reading and there shall be no smell of gas
It is Steve
yes but its excepted that within tolerance leaks are allowed on appliances with no smell or are you talking about pipework only tam?
Not after a reported leak mark including appliances
theres probably a assumption in that reg that a reported leaks come after a smell of gas,its been traced to a appliance within tolerance or not
It applys to all reported smells of gas whether reported to a private gsr guy or an esp.
Once it has been reported as an escape it is then down to you to find it or make safe.
so where does permited drop come in to the equation once ive found a drop its officially a reported leak as i would note it on paperwork therefore by your interpretation i cant then leave it