The difference in calorific value between natural gas and LPG are huge. When doing calculations we are told to use 38.7 MJ/m3 for natural gas as an average but I cant find an average for LPG. Data says its between 90 and 95 so average is 92.5. op said he got a reading of 0.87 m3/hr so using these numbers if we do the calculation using the natural gas formula we get 0.87 x 38.7 / 3.6 = 9.35kw. if we do the calculation using the lpg formula we get 0.87 x 92.5 / 3.6 = 22.4kw which is still a bit low but when dealing with caravans keeping the boiler on high rate for 2 mins isn’t always easy. Dhw flow rate and small heating load can mean boiler wont stay on high rate for that long. Yes I am GSR just don’t have the badge
  • Agree
Reactions: ShaunCorbs
As Shaun said its unsual to have a meter on a caravan site unless it's bulk storage supplied directly by the site.
What is the question? Have you just installed the morco? Was it new?
There is some by me in Staffordshire where the whole site is ran on G20 mate. (75 static vans)