Thanks, John, for the reply, it's interesting every time to see what your thoughts are...
I presume to check that the pump is on the flow side of the boiler is by feeling where the heat goes...
Whenever I've checked, the first pipe to give off heat is the one below the pump, which should be correct one as the arrow on pump is pointing upwards and the arrows on the two-way valves are pointing away from the pump...
Getting rid of air is a questionable one as I can't find any air anywhere but always have a suspicion that air is trapped somewhere.
- One interesting thing I have seen time to time with the new gauge below the expansion tank is that, when I let the system cool down I see the pressure drop on the gauge, I then top the system back up, it will rise rapidly, going from say 0.5bar to 1.5bar, then I turn the system on to heat for a bit, stop it, let it cool down and then again I see the pressure drop to 0.5bar, then I top up again... I had to repeat this process numerous times on Thursday (after putting the ABV back and changing the TRV bodies) till eventually it stopped occurring... However, yesterday when playing around, a few times I let the system cool down to then find myself with a pressure drop... which I then filled again... repeating a few time... It got me questioning whether the filling loop which is using 10mm flexible braided hose, is too narrow and perhaps is introducing air into the system... Being that the water entering under 3bar of pressure is separating as it is forced through the 10mm hose... I'm sure I've read that this can happening...
When you say about up/down radiators not heating together, I'm not sure if that is the case or maybe I have described it incorrectly...
Both upstairs and downstairs are heating up, just I would describe it as not in balance... That is that the radiators don't have equal heat on flow/return and some struggle to have heat when the pump is on lower settings...
- I thought that is a typical description of unbalanced radiators... Have I misunderstoood?
FYI, here are some numbers I took yesterday when trying to manually balance with the pump on:
- I think the system had been heating around 10/15 mins, I didn't note it down, I can't remember which pump setting I had it on, possibly CC at 65%, I would need to repeat to be 100%.
Isolating valves either side of PRV... What valves, there aren't any that I see... I also believe that have isolating valves should not be either side to ensure the PRV isn't accidently isolated... Can you point out to me what you are seeing?
- I was considering putting a service valve below the expansion tank to allow correct testing of the air side of expansion vessel.
When I pressure tested the air side of the expansion vessel, I had to drain down the water to isolate it...
- Altecnic (Caleffi) tech support advised:
Pressure settings: 1.6bar air side & 1.4bar system side.
I asked about the fact that the pressure gauge doesn't go up with heat and got told that was correct behaviour...
I asked to make sure gauge & vessel were the right way up.
I also asked about air in the system.
It looks like at some point, the conversation stopped, I probably got distracted and forgot about it... So if need be I can go back to them to ask further questions...
How do I check the MVs are opening fully?
- They are both definitely opening, % wise, no idea how to check...
- However, I noticed yesterday that the MV to upstairs was buzzing, which in my mind is an indication that it is starting to fail. In the past one of the MVs failed, I think it was the upstairs previously as well... I know the downstairs one was plumped in backwards, which I only noticed, had corrected in Oct 2018.
- If you think it is wise, I can always do as I said previously, which is take out one of the MVs, so only have one MV for the whole house.... Guess it would then rule out a number of potential issues... would require a little change to the pipework...
Ooohhh, I like your idea of isolating each radiator one at a time, to bleed them... Tomorrow, I will do this, record the numbers and we can discuss results...
- I do remember watching a youtube video which someone did this... What they also did was keep the fill loop open and controlled via PRV, they then isolated each radiator, opening the lockshield drain off to flush air that was trapped out... I actually bought a PRV to do this very thing. However, I didn't actually implement this as I hadn't all the connections to implement and then again got distracted... So, if needed, can do this later...
Anyway, now I'm waffling on, so thanks for the advice, I'll come back to you tomorrow.
I presume to check that the pump is on the flow side of the boiler is by feeling where the heat goes...
Whenever I've checked, the first pipe to give off heat is the one below the pump, which should be correct one as the arrow on pump is pointing upwards and the arrows on the two-way valves are pointing away from the pump...
Getting rid of air is a questionable one as I can't find any air anywhere but always have a suspicion that air is trapped somewhere.
- One interesting thing I have seen time to time with the new gauge below the expansion tank is that, when I let the system cool down I see the pressure drop on the gauge, I then top the system back up, it will rise rapidly, going from say 0.5bar to 1.5bar, then I turn the system on to heat for a bit, stop it, let it cool down and then again I see the pressure drop to 0.5bar, then I top up again... I had to repeat this process numerous times on Thursday (after putting the ABV back and changing the TRV bodies) till eventually it stopped occurring... However, yesterday when playing around, a few times I let the system cool down to then find myself with a pressure drop... which I then filled again... repeating a few time... It got me questioning whether the filling loop which is using 10mm flexible braided hose, is too narrow and perhaps is introducing air into the system... Being that the water entering under 3bar of pressure is separating as it is forced through the 10mm hose... I'm sure I've read that this can happening...
When you say about up/down radiators not heating together, I'm not sure if that is the case or maybe I have described it incorrectly...
Both upstairs and downstairs are heating up, just I would describe it as not in balance... That is that the radiators don't have equal heat on flow/return and some struggle to have heat when the pump is on lower settings...
- I thought that is a typical description of unbalanced radiators... Have I misunderstoood?
FYI, here are some numbers I took yesterday when trying to manually balance with the pump on:
- I think the system had been heating around 10/15 mins, I didn't note it down, I can't remember which pump setting I had it on, possibly CC at 65%, I would need to repeat to be 100%.
Isolating valves either side of PRV... What valves, there aren't any that I see... I also believe that have isolating valves should not be either side to ensure the PRV isn't accidently isolated... Can you point out to me what you are seeing?
- I was considering putting a service valve below the expansion tank to allow correct testing of the air side of expansion vessel.
When I pressure tested the air side of the expansion vessel, I had to drain down the water to isolate it...
- Altecnic (Caleffi) tech support advised:
Pressure settings: 1.6bar air side & 1.4bar system side.
I asked about the fact that the pressure gauge doesn't go up with heat and got told that was correct behaviour...
I asked to make sure gauge & vessel were the right way up.
I also asked about air in the system.
It looks like at some point, the conversation stopped, I probably got distracted and forgot about it... So if need be I can go back to them to ask further questions...
How do I check the MVs are opening fully?
- They are both definitely opening, % wise, no idea how to check...
- However, I noticed yesterday that the MV to upstairs was buzzing, which in my mind is an indication that it is starting to fail. In the past one of the MVs failed, I think it was the upstairs previously as well... I know the downstairs one was plumped in backwards, which I only noticed, had corrected in Oct 2018.
- If you think it is wise, I can always do as I said previously, which is take out one of the MVs, so only have one MV for the whole house.... Guess it would then rule out a number of potential issues... would require a little change to the pipework...
Ooohhh, I like your idea of isolating each radiator one at a time, to bleed them... Tomorrow, I will do this, record the numbers and we can discuss results...
- I do remember watching a youtube video which someone did this... What they also did was keep the fill loop open and controlled via PRV, they then isolated each radiator, opening the lockshield drain off to flush air that was trapped out... I actually bought a PRV to do this very thing. However, I didn't actually implement this as I hadn't all the connections to implement and then again got distracted... So, if needed, can do this later...
Anyway, now I'm waffling on, so thanks for the advice, I'll come back to you tomorrow.