Sorry I hadn't realised in was important.
Grant Vortex Utility 15-26 set to 23. Install in 2005.
Grant Vortex Utility 15-26 set to 23. Install in 2005.
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
There are only 10 rads in the house, so I doubt if they add up to 23kW; probably not much more than 15-20kW. As oil boilers do not modulate, the boiler will be cycling wth a 65/35 on/off period.With rads only on and assuming they are emitting/absorbing that 23 kw then a flow rate of ~ 18/20 LPM should give a rad(s) delta T of ~ 17C so either PP2 or CP1 might do the job.
You are correct, the Rads are about 16kW and the HW is 14.5kW. So I do get a bit of cycling. The excess covers the overlap when both are calling for heat. I have run the boiler at 19kW, but when the smaler burner burnt out, it was replaced with the std one which then give 23kW. Maybe I should consider the saller burner at the next service.There are only 10 rads in the house, so I doubt if they add up to 23kW; probably not much more than 15-20kW. As oil boilers do not modulate, the boiler will be cycling wth a 65/35 on/off period.
I have also re-checked the numbers, and CP1 = 20W; CP2= 35W. Some of the thermostatic valves are now shut as the weather is warm (Devon is 25C)
Where do you get your numbers from:Something else that caught my eye there in the numbers, see attachment, if you look at the head/flowrates for CP2 and CP1, CP2 is showing a flow rate of 0.95 m3/[email protected] and CP1, 1.1 M3/hr@3M, maybe I'm reading the curves incorrectly but for the same system resistance these two readings are incompattible?, a flow of 1.1 M3/h@ 3m = 1.35 M3/[email protected] or 0.95 M3/[email protected] = 0.78 M3/hr@3M.
I got bored and switched off!Wow this is a proper pump love in isn’t it
I thought that's what you had done; just wanted to be sure.The (very) top table (composite file) are my results from the below:
etc etc
I thought that's what you had done; just wanted to be sure.
Don't forget that when the pump is in a constant pressure mode it will vary the output to maintain the required pressure. The fact that the pressure may be too high or too low is irrelevant.