We had a wet UFH system installed a couple of years ago. Two weeks ago we had vinyl tiles laid. The instruction from the flooring guy is to start the UFH at 5 degrees and increase by 5 degrees per day until we reach a comfortable temperature. Also, instructions from the flooring company read 'A maximum sub floor temperature, at the adhesive line, of 27 degrees should never be exceeded'

I am confused what I need to do in that the control on the manifold that I think I need to alter will only turn down to about 20. Also, prior to the vinyl tiles being laid, this control was set about 40. So, how will 27 now be warm enough ?

Is this the right control to alter ? What am I not understanding ? The photo I have attached is the control which I've turned down as low as it will go, which I think is about 20. Thanks in advance for any help.
 

Attachments

  • Screenshot_20211105-052146_Photos.jpg
    Screenshot_20211105-052146_Photos.jpg
    135.3 KB · Views: 33
Is this the right control to alter ? What am I not understanding ? The photo I have attached is the control which I've turned down as low as it will go, which I think is about 20. Thanks in advance for any help.
Another couple of photos (or a description) so we can know what it's connected to, if possible please.
 
The manifold control is showing water temperature not floor temperature.
Turn it as low as it will go to start then increase in increments.
 
If you ran it at 40 and you now want to run it at a lower temperature- it will simply need to be ‘on’ for longer. Floor at 27 can give room at 20 no problem.
 
The instruction from the flooring guy is to start the UFH at 5 degrees and increase by 5 degrees per day until we reach a comfortable temperature.
5°C is refrigerator temperature. They must have meant to say start at 25°C and increase by 5°C per day.
 
Another couple of photos (or a description) so we can know what it's connected to, if possible please.
Thanks Chuck. It's sorted now in that I rang the vinyl tile manufacturers this morning who said because the floor has been laid for 2 weeks already, the adhesive should have already bonded. So, can start the system at the lowest setting (which is around 20) and increase slowly. Thanks for your help.
 
5°C is refrigerator temperature. They must have meant to say start at 25°C and increase by 5°C per day.
Hahaha .. Well, it certainly feels like a freezer in here at the moment, so Yes, having thought about it 5 degrees is like a fridge. I've started it on about 20 degrees. Thanks Chuck.
 
The manifold control is showing water temperature not floor temperature.
Turn it as low as it will go to start then increase in increments.
Snowhead - Sorry if this is a daft question but how do I know what the floor temperature is ? Is there a gadget / some sort of thermometer that I can use ? Thanks
 

Official Sponsors of Plumbers Talk

Reply to the thread, titled "Help with wet under floor heating temperatures" which is posted in Water Underfloor Heating Advice on Plumbers Forums.

We recommend City Plumbing Supplies, BES, and Plumbing Superstore for all plumbing supplies.

Thread starter

Joined
Member Type
DIY or Homeowner

Thread Information

Title
Help with wet under floor heating temperatures
Prefix
N/A
Forum
Water Underfloor Heating Advice
Start date
Last reply date
Replies
11

Thread Tags

Thread statistics

Created
Newbie100,
Last reply from
Newbie100,
Replies
11
Views
2,399

Weekly or Monthly Email Digest

Back
Top