All the cylinders in the Telford range for gravity circulation are shown as having either 28mm or 35mm id coils"
Does it state/implicate corrugations or not?.
No, copy appended below
Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
All the cylinders in the Telford range for gravity circulation are shown as having either 28mm or 35mm id coils"
Does it state/implicate corrugations or not?.
7. Bathoom radiator loop providing a low impedance path in parallel with the cylinder coil.I am trying to compile a full list of possible reasons for the replacement cylinder not getting any heat. Here is my list so far:
[...]
One of our people fitted a Replacement Telford Indirect Vented cylinder (type G 9E) today in a three storey property in Oxford. This was a pumped system. However, looking at the literature and the instructions et al that came with the cylinder (delivered to us direct by Telford) - it is fitted with a 28mm inside diameter coil. From the chart ( which sets out the full standard vented Telford range (models 0 to 14 plus 9E)) in the instructions, There are only two models in the standard Telford range the 0 and 1 (96litre and 72 litre respectively) that are fitted with a 22mm inside diameter coil. It is stated in the notes that these cylinders are for pumped primary’s only.
All the cylinders in the Telford range for gravity circulation are shown as having either 28mm or 35mm id coils
7. Bathoom radiator loop providing a low impedance path in parallel with the cylinder coil.
Did you change the lockshield setting on that radiator at some point? If so, you might have left it too open.
Personally, I'd have fitted a circulating pump about a year ago. It doesn't take much to stop gravity circulation working and diagnosing the cause is often a waste of time because the remedy is mostly likely to be 'fit a circulating pump...' anyway.
Have the horizontal runs been checked after the new install? Is it possible the horizontal run could have been disturbed and pushed down under the floor causing a drop in the pipework rather than a steady rise. As I think other's have said the distance the gravity circs are run Horizontally seems quite large - however if it's worked for 50 years before must be OK
(And Bathroom rad works)
I had a very similar issue with my in Laws log burner and heat sink rad that was fitted by a previous installer. The rad would always work however the coil in the cylinder wouldn't - I concluded before ripping the thing out was that the circs to the cylinder didn't have great enough horizontal gains as the pipework was clear.
I've replaced old gravity cylinders with cylinders that are meant to be fully pumped before now (Due to what was needed and future upgrades coming) and never had any issues with them circulating on gravity systems.
What was the issue with the old cylinder? Did it leak or was a leak developed on the coil and CH & HW water was mixing?
You can, I've done it a few times.I don’t think that I can post a PDF on this site (But may wrong on that).
If you haven't already, you could try saving it on a drive, then click on the file name to attach it.You can, I've done it a few times.
Neville,
All the information is in the Telford 2019 technical product catalogue 40. If you cannot source a copy PM me and I will email you a PDF copy. I don’t think that I can post a PDF on this site (But may wrong on that).
One of our people fitted a Replacement Telford Indirect Vented cylinder (type G 9E) today in a three storey property in Oxford. This was a pumped system. However, looking at the literature and the instructions et al that came with the cylinder (delivered to us direct by Telford) - it is fitted with a 28mm inside diameter coil. From the chart ( which sets out the full standard vented Telford range (models 0 to 14 plus 9E)) in the instructions, There are only two models in the standard Telford range the 0 and 1 (96litre and 72 litre respectively) that are fitted with a 22mm inside diameter coil. It is stated in the notes that these cylinders are for pumped primary’s only.
All the cylinders in the Telford range for gravity circulation are shown as having either 28mm or 35mm id coils
“Size of the primary heater” is the Internal diameter of the coil in mm.
The connections on Telford vented cylinders are normally all the same - G1 which has a Nominal Bore of just under 30mm irrespective of the internal coil internal diameter.
in essence, you cannot determine the internal coil diameter from the external connection. Unless of course you have long thin fingers!
The external fittings are shown in the last two columns of the chart that you have posted
My understanding is that G is the German/ISO designation equivalent to BSPP. These were specified for thick steel gas pipes and so tend to be a size larger than copper. G1 was originally for a pipe with a 1 inch internal diameter.
Whilst I am not saying you are wrong, I continue to have two problems with this chart:
1 - it is for copper cylinders and not stainless
2 - internal coil diameter is not clearly stated.
I am a retired Chartered Electrical Engineer and am looking for information about the necessary conditions for gravity primary circulation in a 28mm domestic indirect vented hot water circuit.
Until recently I have fitted Hercal cylinders in my house and they always worked without any difficulty. I have now replaced the old copper Hercal with a stainless Telford cylinder but cannot get any primary circulation.
I have flushed all sections of pipework and tried bringing the boiler up to boiling point but there is still no hot flow down the coil. I can only assume that there is an air lock resulting from a coil which probably does not go consistently down all the way. It may not be helped by the non-smooth very flexible pipe. Perhaps a corrugated surface is not particularly good at promoting downward flow of water combined with chalk and cast iron particles whilst encouraging upward flow of trapped air.
I would be grateful for any advice or pointers to sources of information about this.
Neville
A member of my family is having the same problem as you. Gravity fed boiler.28mm sloping pipe from boiler to cylinder. She had no heating too. The boiler had not been on all summer and when she recently tried it, had no hot water or heating. The boiler was installed in 1977. I found that the radiators were full of sludge and that this had caused the heating pump to jam. However, there are still no hot water. The 28mm flow pipe was stone cold. I then flushed the heating water for 5 mins with the drain connection on the base of the Ideal Vulcan boiler where there is a drain cock. Only 5 mins of gravity fushing and the flow pipe immediately got hot. I left because it was getting late and later found that she still had no hot water. I am going round to power flush the system. I think there is a build up of sludge at the base of the flow pipe. Will be carrying the flush out next week. I think a power flush with cleaner will do the trick removing any air lock and sludge ( just the risk of a leak but at least the problem will hopefully be cured ).Not yet - too many other things going on.