Remeha Avanta+28C, I went to do a landlords and found that the front case was damaged, it had the two tabs that secure the front on to the main body broken off so no way to securely fit the front back on. As this case front should form a room seal & acts as an air box I stuck on a do not use label, turned it off and AR it. filled out the warning notice & I explained to the tenant that if it is used it could cause a danger in the future if the combustion seal becomes defective or if the inner flue corrodes the POC could get pulled back into the boiler and out of the broken case seal into the room if left like that & they happily signed the warning notice. Also the Exp vessel was leaking out of the schrieder valve onto the electrics and there were signs of corrosion on the main body case floor around the hydrolic block. the pressure gauge did not work & the PRV is letting by due to knackered EXP vessel. I suggested due to the age & condition of the boiler it would be better to replace rather than repair. 2 days later I get an email from Gas Safe saying that a complaint has been made about my work & I now have to meet a Gas Safe inspector at the job on the 19th at 1pm to go through it with him and the Landlord. So an afternoon with out pay!
Now I am second guessing myself & wondering if I was too harsh or wrongly AR'd it. What would you guys have done?
Now I am second guessing myself & wondering if I was too harsh or wrongly AR'd it. What would you guys have done?